immersion query

yep i believe between 17-19 is the OK range for a 3KW heater element. Glad I got to test it properley now from finding the right range. Thanks for your help.

And as continuity was between L and T then all should be ok.

So the no hot water problem is because of what?!!!! Ahh!
 
you have proved continuity on element by doing a ohms test.
is their power to the stat ?
 
i have proved the switch is working by testing continuity between L and T terminals (should i do a resistance test here also). Then I did the resistance test and got 19.6 reading. So proves the element is fine.

(although working out, using the WIV and VIR triangles! I should have 17 ohms for a 3kw heater. 19 is slightly over that.)
 
forget the continuity test.
use the volt meter.
what voltage is going into the stat ?
what voltage is coming out the stat ?
 
providing you don't touch the cable,probes and you have it set to volts ac.
stick it on 600
 