But, if you start with all the LSVs open (as in this case), and the pump turned up to try and get cold radiators hot, balancing will reduce the boiler return temperature and allow flow rate to be reduced. I can see that boilers can need a minimum flow rate, so DIYers shouldn't take it too far and should be wary of turning down the pump speed. I suspect that boiler manufacturers' instructions would include a maximum temperature differential across the boiler that corresponds to minimum specified flow rate at full chat.The purpose of balancing is not reduce the flow rate and lower the return temp but to ensure that the correct flows rate and return temperatures are obtained.
Those were the instructions in one TRV commissioning guide (another thread).Quarter turns is a large amount.
I disagree. As the boiler is turned up to cope with cold weather, the heat output from radiators not on TRVs will increase. Assuming constant flow rate, increased heat lost from the water must increase temperature drop.That will only be true if the flow rate decreases as the feed temperature increases.
I'm getting the impression that 'proper' commissioning is more complicated than balancing radiators to have 11°C temperature drops if you need to ensure a minimum flow through the boiler. On a small system, this flow should be spread between all the radiators according to their nominal outputs. This might require 'higher than designed' radiator flow rates and, consequently, reduced temperature drops. Otherwise, an ABV will have to supply the extra flow rate, even with all the TRVs open.
However, even crude DIY balancing can fix the problem of larger and/or more remote radiators not heating up properly. The main domestic requirement is to get all the radiators hot as quickly as possible. To this end, I suggest at least one radiator (most difficult to heat) should have its LSV wide open. All the other radiators should have their LSVs adjusted to match the temperature drop of this 'most difficult' radiator. Finally, if the temperature drop across the most difficult radiator is more than 11°C, the pump speed can be increased.