independent ceiling span of 4m, 400 centres, size of joist?

Discussion in 'Building Regulations and Planning Permission' started by Casterbridge, 23 Jul 2013.

  1. Casterbridge

    Casterbridge

    Joined:
    5 Jun 2012
    Messages:
    119
    Thanks Received:
    0
    Country:
    United Kingdom
    Independent ceiling at 400mm centres, span of 4m. Will hold 2 x 12.5mm fireboard - total plasterboard weight 20kg/m3. Also some insulation taking the total static load to less than 30kg/m3. No live load as the floor will remian in situ above.

    Are there any tables for the size of ceiling joists for the ceiling for c16 or c24 timber. I can only find floor joists, not ceiling joists (I assume the pure static load will allow me to use smaller joists that for a floor?)
     
  2. Sponsored Links
  3. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    38,158
    Thanks Received:
    2,447
    Location:
    Staffordshire
    Country:
    United Kingdom
    Use 100mm x 50mm with a central binder strapped to the existing ceiling joists.
     
  4. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,581
    Thanks Received:
    1,429
    Location:
    Manchester
    Country:
    United Kingdom
    The older editions of Approved Document A have the tables for ceiling joists.

    Looking at mine it says 7x2s C16 would be OK for 3.72 m for dead load 0.25 to 0.5 KN/sq m. (your 2 layers pb'd will fall in this range).

    But these figures allowed for a small live load (loft storage) of 5lbs/sq ft,
    so you should be well-OK on a 4m span with no load other than dead load.

    Or cheaper as Noseall said to use smaller joists and suspend mid-span?
     
  5. Casterbridge

    Casterbridge

    Joined:
    5 Jun 2012
    Messages:
    119
    Thanks Received:
    0
    Country:
    United Kingdom
  6. tony1851

    tony1851

    Joined:
    23 Feb 2012
    Messages:
    9,581
    Thanks Received:
    1,429
    Location:
    Manchester
    Country:
    United Kingdom
    That's about right - my table for C24 on that span says 3.99m.
    But C24, although a stronger timber, does have a tendency to twist slightly - more so than C16.
    If you don't want to use hangers, just use 7x2s @ 400.
     
  7. freddiemercurystwin

    freddiemercurystwin

    Joined:
    21 Jan 2007
    Messages:
    18,576
    Thanks Received:
    2,036
    Location:
    Devon
    Country:
    United Kingdom
    The tables and the info on the PDF you linked to is all taken from the original TRADA span tables so is reliable. 7x2's as mentioned will be fine.

    The old 1992 version of the building Regs Part A is available to view on the Planning Portal.
     
  8. Casterbridge

    Casterbridge

    Joined:
    5 Jun 2012
    Messages:
    119
    Thanks Received:
    0
    Country:
    United Kingdom
  9. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019