Hi advice please
Photo 1 shows the original cabling to an electric oven
Photo 2 shows an induction hob added
Is this acceptable with both working off a single cooker switch and a 32A breaker?
I know part of the induction hob wiring will be outside the outlet plate but it will be inaccessible behind the oven.
 

Attachments

  • IMG_1471.jpeg
    IMG_1471.jpeg
    569.3 KB · Views: 6
  • IMG_1472.jpeg
    IMG_1472.jpeg
    530.8 KB · Views: 6
No not acceptable, single insulation shouldn't be visible when the lid is put back on.

Looks like theres already 2 appliances connected, what are they and whats the combined kW rating of all 3?
 
Currently there is a single oven and grill (rating unknown) and a socket (unused and can be disconnected) so there will only be the 2 appliances. The induction hob is 7200kw.
I could clip the induction hob cable so the single insulation sits inside the cover.
Would this be acceptable?
 