Hi

I wish to add some sentinel x100 inhibitor into my system because it does not have any in there.

I purchased a can which is designed to fit onto the filling loop.
Says the system should have less than 2.3bar in it (I was going to take it below 1)

The way my system has been plumbed, means this filling would need to go thru the one way valve.

Would there be enough pressure in the can to overcome the one way valve do you think?
or am I wasting my time trying?
 
I’d take it down to 0 bar so it should go in easily. Surely if it’s a filling loop, the 'one way' you mention would be into the system?
 
yes is the simple answer it will go in , not too convinced that those types actually work though
 