Install of new wifi thermostat

Joined
7 Mar 2023
Messages
9
Reaction score
2
Country
United Kingdom
Hi all I have just had a electrician to fit a new wifi thermostat but we can't seen to get the control box to communicate to the boiler
The boiler is a glow worm -BETACOM 3 30C
 
Sponsored Links
This is the wifi thermostat
 

Attachments

  • 16781973570138524955250955368403.jpg
    16781973570138524955250955368403.jpg
    176.1 KB · Views: 34
we can't seen to get the control box to communicate to the boiler
'We', as in you and the electrician, can't get the box to communicate with the boiler?

Are you replacing an existing thermostat?
If so, the thermostat may have been 24V switching, or 230V mains switching. It would not be good if they were mixed up!

Screenshot_20230307-143339_Adobe Acrobat.jpg

The wiring on the boiler is straightforward and troubleshooting a dodgy receiver should also be straightforward - perhaps you need a new electrician! ;)

Edit:
Found a manual for the 'Heating Thermostat'
Screenshot_20230307-144434_Adobe Acrobat.jpg

Manual attached...
 

Attachments

  • 25239397.pdf
    1 MB · Views: 128
Last edited:
Sponsored Links
Hi it is a new install as when the new boiler was installed he didn't connect the old one up the electrician has gone as he couldn't get it working
 
The control box
 

Attachments

  • 16782086334627790798109724133902.jpg
    16782086334627790798109724133902.jpg
    144.7 KB · Views: 42
And that is connected to the Ebus
 

Attachments

  • 16782087716516517707137721672753.jpg
    16782087716516517707137721672753.jpg
    191.4 KB · Views: 32
If your Broadband router is modern, it will have two different paswords and adresses, you can only use the 2.4GHZ setup the default is usually the 5.0 GHZ
 
Broadband side is all good thanks
So the 2 wires from con & No go into the 24v switching not the ebus ?
 
that is your problem remove the red link in 24v switching and put the wires in there not the ebus
:)
perhaps you need a new electrician! ;)

So the 2 wires from con & No go into the 24v switching not the ebus ?
Yes, the connections from "Com" - common and "NO" - Normally Open, connect to the 24V/RT connections on the boiler.

The ebus connection is there for thermostats that 'talk' to the boiler through a serial data link, not just the on and off switching, that your new receiver uses.

you can only use the 2.4GHZ setup the default is usually the 5.0 GHZ
...and a lot of the default setups have both bands sharing the same SSID - that's where many problems start :(
 
just out of interest, did you supply this stat or was it supplied as part of the boiler install ?
 