Thanks confirming. In that case, you presumably understand that it is not saying (at all, let alone 'clearly and unequivocally') that this is the only acceptable design.
I understand that it is clearly and unequivocally saying that if you want to use the provisions of 433.1.5 to design a ring final circuit deemed to comply with 433.1.1 then the I
z of the cable must be at least 20A.
You do not.
There may be ways in which a circuit not immediately in compliance with 433.1.1 can be justified by the designer, but if the I
z of the cable is not at least 20A then, clearly and unequivocally, the provision for RFCs in 433.1.5 is not one of them.
I don't know about you, but I am not a professional designer of electrical installations, so I'll leave it to those who are to comment on whether they feel that, in appropriate circumstances, it would be reasonable/acceptable for them to exercise judgement such as we are discussing. I think what you may be overlooking to some extent is the question of 'design current'. If a designer believes that the anticipated load is low, then I think such judgements might become more reasonable.
Stop wriggling.
This is a ring final circuit in a domestic dwelling.
When ricicle told the OP (who is not a qualified designer) that he could decide that he had "
a properly designed ring final circuit in which the cable will share load evenly with a theoretical maximum of 16A on any one leg which is a fraction more than 50% of the current carrying capacity of 2.5mm² so is not going to be a problem bearing in mind that ring finals rarely spend very long, if ever, at their maximum allowable design current", and I challenged him on that, because of 431.1.1, YOU said "
I do not believe that in any way prevents a designer producing a design which satisfies 433.1.1 without satisfying the requirements of 433.1.5's deemed-to-satisfy provision."
And you've kept on in that vein, despite all your disclaimers about not being a qualified designer and despite recognising the difficulties of establishing I
b for final circuits serving BS 1363 accessories.
The OP (who is not a qualified designer) came here for advice.
YOU supported the notion that he could install a circuit which did not comply with 433.1.5
So
YOU have to justify that, not say "Oh well I'm sure that some people might sometimes be able to". Or take your ideas off to another of your dedicated eristic threads where they can safely be ignored.
You are asking me questions which only an experienced designer of electrical installations can really answer,
And I'm asking them because of your support for the idea that the OP could install a circuit which does not comply with 433.1.1 and which does not qualify for the deemed compliance provided by 433.1.5.