By anaolgy with 433.1.5 that would (to my mind) make total design sense, and I'm sure would be at least as safe as the deemed-to-satisfy 2.5mm²/32A MCB RFC (as I said, I suspect a designer could probably justify a 26A MCB, if (s)he could find one). However, I suspect there may be dissenting voices here.Use 2.5mm for the ring and fit a 20 amp MCB or RCBO, job done
Why on earth are you trying to put those words incorrectly into my mouth? If one wants to use the deemed-to-comply provision of 433.1.5 to satisfy 433.1.1, then one obviously has to have a cable of at least 20A CCC. That's what the deemed-to-satisfy provision says!
I was merely pointing out that 433.1.5 does not "clearly and unequivocally call for the cable to be capable of carrying 20A".
Yes you have, over and over again.I have at no point suggested that the op should adopt a non-conventional design.
That is the purpose of this topic.Im installing a new ring circuit in a renovated Bungalow.
Right down the nitty gritty ok i am running the cables through the joists above the downstairs ceiling and there is going to be 240mm insulation between the ceiling and floor upstairs do i have to use 2.5mm cable or do i have to step it up to a larger size for temperature reasons any feed back would be appreciated THANKS IN ADVANCE!!!!!!
INThe only reason I got involved was to point out that you appeared to be making an incorrect assertion that the deemed-to-satsify provision of 433.15 represents the one and only acceptable basis for designing an RFC.
andIf one wants to use the deemed-to-comply provision of 433.1.5 to satisfy 433.1.1, then one obviously has to have a cable of at least 20A CCC. That's what the deemed-to-satisfy provision says!
If you need a hint, try studying the conditional clause at the start of the first one.I was merely pointing out that 433.1.5 does not "clearly and unequivocally call for the cable to be capable of carrying 20A".
Yes, I agree that it indicates a way in which such circuits can be allowed to exist.The whole point of 433.1.5 is to allow ring final circuits which would otherwise contravene 433.1.1 to exist.
I don't doubt that is largely true, although I'm sure there are some exceptions. Nor (and this is going to be controversial) do I really think that electricians should be expected to do 'from first principles' design. In many walks of life, we've seen blurring of the distinction between designers and 'do-ers' and I'm far from convinced it's a good thing - for a start because (a) it usually ends up as an imperfect compromise and (b) it often represents inefficient use of dfferent skill sets.Trained electricians* are universally** incapable of designing ring circuits 'outside the box'.
Again, I more-or-less totally agree with all that. I don't think that 433.1.5 is actually a problem. Indeed, it is the one part of the regs which allows an electrician to install an RFC on a 'cookbook' basis without having any knowledge of how the design came about, or how they would set out to design an RFC 'from scratch' themselves.Trained Indeed most of them are utterly unaware of the existence of Reg 433.1.5 and have never been taught any relevant electrical theory regarding the design of rings. This is mostly because their lecturers do not understand either and because rings are installed for one reason and one reason alone - it's been done, without thought or question, since 1947.
Even though they have 'done us proud' (despite dramatically increasing numbers of electrical appliances to be supplied) in the UK for around 60 years, I'm not really a lover of rings; I'm sure they are an example of one of those things (like tobacco and alcohol) which would never have been allowed if they had first shown their faces in the later stages of the 20th century! This particular thread has not been about the pros and cons of rings, and BAS has not attempted to convince me, in this thread, that they are not the ideal choice for socket circuits. In any event, as I said, I don't need convincing of that.Because of this general ignorance, rings should not be the design of choice for socket circuits, as B-A-S has spent some considerable time trying to convince you.
Given that adequately trained people are generally not involved in the design process of individual installations, that's a very reasonable attitude. I guess some of this comes back to the inadequacy of the regs - in only offering one deemed-to-supply design for an RFC. If it offered a range of options, electricians would thereby be able to select the one that bst suited the circumstances without needing the engineering knowledge to be able to design one from scratch. As is apparent from the question which started this thread, this is now a particular issue given that installation methods can result in the CCC of 2.5mm² T&E falling below 20A - which currently means that the regs offer no explicit solution which would enable such cable to be used in a ring.I'm not saying (and have never said) you should never use a ring, but I am adamant that our electricians install rings precisely because they do not understand clearly what a ring is all about.
I wasn't debating anything for its own sake - I was trying to get ricicle and JohnW2 to see that they were wrong to suggest to the OP that a solution might be to install a ring final which does not comply with 433.1.5.
Because of this general ignorance, rings should not be the design of choice for socket circuits, as B-A-S has spent some considerable time trying to convince you.
Many thanks for that interesting historical information. It has caused me to think again, and modify my position somewhat (see below).In the absence of any genuine information to the contrary we have to assume that the IEE changed 433-02-04 from requiring Iz to be ≥ 0.67xIn to requiring it to be ≥ 20A in order to be deemed to comply with 433-02-01 for a reason. The 0.67 ratio may once have given some support for a "non-standard" ring (even though the standard then was still an OPD of 30/32A), but that support was explicitly removed in February 2002.
... even if the electrician can see that a ring final with a 20A OPD and a cable with a CCC ≥ 13.4A is just as safe as a 32-20 one ....