Say you had a cable running horizontally through floor joists without any thermal insulation (assuming horizontal cable support requirements were met), how is one supposed to know how much to de-rate the cable by and what the de-rated current carrying capacity is for a given conductor size.
Based on Table 4D5 in BS7671 does not mention anything about 70c thermoplastic insulated sheathed flat cables with CPC running through joists in free air, does that mean it's not a permitted installation method?
Maybe I'm missing something here, but I'm sure I have seen cables run for several meters through the middle of joists. Assuming no thermal insulation and a single circuit (i.e. no cable grouping), what is the current carrying capacity of T&E cable installed in such a way? Same as method C/clipped direct, or something else?
Any reg numbers to help answer my question above would also be helpful.
Regards: Elliott.
Based on Table 4D5 in BS7671 does not mention anything about 70c thermoplastic insulated sheathed flat cables with CPC running through joists in free air, does that mean it's not a permitted installation method?
Maybe I'm missing something here, but I'm sure I have seen cables run for several meters through the middle of joists. Assuming no thermal insulation and a single circuit (i.e. no cable grouping), what is the current carrying capacity of T&E cable installed in such a way? Same as method C/clipped direct, or something else?
Any reg numbers to help answer my question above would also be helpful.
Regards: Elliott.