Installing new cable for cooker - info please
15 May 2007
Hello
Putting a new run of cable from CU to cooker (3kw).
Placing into vertical chanel to l/hand of cooker and then going towards the right at about half the height of the cooker.
What do i terminate into behind the cooker? And from there how do i connect to the cooker point?
Cheers
You can't have a concealed cable with a change of direction unless there is something to indicate the cables presence along both it's runs. Could you draw a diagram of the run so we can advise whether it is acceptable?
You are aware that new circuits are notifiable aren't you?
Since it is only 3kw just terminate into a 13A FCU and connect the flex from the cooker into the load terminals.
Cable run is 43cm in from the lefthand wall in a vertical chanell. At a height of 56cm from the floor the run will head right for 46cm to be in position for the cooker.
Maximum depth of chanell will be approx 3.5cm
This run will end up behind kitchen cabinets
Will the FCU be positioned beneath the worktops or above? Either way how, physically, will the cable from the cooker enter the FCU?
Forgot to say i have a new 45amp cooker control unit for the install.
As I said previously, you can't have a change of direction unless there is a fitting to indicate both cable routes - put a socket outlet at the bottom of the vertical run, just below where the cable makes a 90 degree turn.
If it feeds just the single electric oven you can have the CCU above the worktop, feeding a cooker outlet plate below the worktop where the oven will be wired. Does the oven come with a moulded plug? If so cutting it off will most probably void the warranty.