Confused. Looking at the regs as I understand a refurb needs to acheive 0.25 w/m2k in ceilings, is that correct.
And can I acheive that with dritherm 32 which is 0.32 w/m2k
According to the updated Part L documents, the U values for existing elements in existing dwellings, the limiting U values will be:
Roofs: 0.16 W/m²K
Walls: 0.30 W/m²K
Floors: 0.25 W/m²K
Problem is the regs state in W/m²K but the spec for different thickness for dritherm is in R value. Here are the specs from the dritherm website.
So what thickness will acheive Floors: 0.25 W/m²K.
Its a kitchen downstairs ceiling I am planning on using the slabs as they will be pushed up from underneath and should self support before I re-board.
Thanks