    This is more of an academic question rather than a specific problem.

    Can anyone explain how insulation resistance tests work? I understand the test procedure and can interpret the results of the tests, but I don't really understand the physics behind how the tests work. Is it that 500v are slung down the conductor and a measurement is made at the other end to see if there has been any voltage leakage along the way.... im puzzled. Purely interested from a physics perspective rather than a real world problem I'm trying resolve.

    Merry
     
  2. Sponsored Links
  3. 333rocky333

    333rocky333

    Joined:
    12 Jan 2008
    Messages:
    8,382
    Thanks Received:
    894
    Location:
    Essex
    Country:
    United Kingdom
    No measurement is taken at the other end, it tests from one end only and measures resistance between the twoleads and whatever they are connected to.
    Not sure how it does it though.
     
  4. crystal ball

    crystal ball

    Joined:
    28 Apr 2004
    Messages:
    5,259
    Thanks Received:
    307
    Country:
    United Kingdom
    Usually on a single phase system IR checks are mad between L-N, L-E. N-E all from the same end
     
  5. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,245
    Thanks Received:
    1,701
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    E/IxR so E which stands for volts so is 500/I which is current = R the resistance, so it measures current but displays resistance.

    Impedance and resistance are simular, but not quite, so although ohms law may show 5 mA should flow, it may well be that 10 mA flows because of inductive and capacitive links.
     
  6. sparxxxx

    sparxxxx

    Joined:
    8 Dec 2020
    Messages:
    197
    Thanks Received:
    20
    Country:
    United Kingdom
    Its a test between conductors, and its measuring any leakage current generated by the tester between eg L and N, the tester computes that leakage current and gives a reading in ohms, the lowest acceptable reading on a 230v circuit is 1MΩ or 1 Megohm (1,000,000 ohms). A reading of less than 1MΩ could be made up of one area of leakage current or many different points. It can be used to monitor deterioration in a circuit by comparing historic readings.

    Although the minimum allowed is 1MΩ, this would be unacceptable on a new installation as its actually an indication of a fault, expected readings should be 100MΩ+ for all new circuits
     
  7. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,530
    Thanks Received:
    374
    Country:
    United Kingdom
    The tester applies a test voltage, measures the voltage and current and calculates resistance.

    I'd imagine the hardest part in designing such a tester would be designing the very sensitive and yet robust (sooner or later someone is going to test a short-circuit) current measurement.

    The tester I used had a maximum reading of 4GΩ At 500V that translates to 125 nanoamps.
     
  8. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,567
    Thanks Received:
    2,550
    Location:
    Bedfordshire
    Country:
    United Kingdom
    It is possible the the circuit generating the 500 Volt test voltage is designed with current limiting to prevent the current being too high for the current measuring circuit. If the current limiting did become effective then the device would have to indicate a failure in some way as the applied voltage would be less than the required test voltage.
     
  9. SimonH2

    SimonH2

    Joined:
    4 Nov 2010
    Messages:
    5,826
    Thanks Received:
    589
    Location:
    Cumbria
    Country:
    United Kingdom
    The voltage generation would inherently be current limited anyway - simply by stepping up battery voltage to 500V (or whatever is selected). Mains powered equipment could be a different matter though !
    As for sensitive electronics, consider that your typical DMM on auto-ranging will go down to it's most sensitive range looking for something to display. Then you go and connect it to anything up to 1000V which it has to detect and auto-range to a higher scale. The techniques have existed for decades, though I don't know enough about the electronics involved to know how it's done.
     
  10. Sponsored Links
  11. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,145
    Thanks Received:
    3,142
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    My Fluke MFT reduces the test voltage as/when necessary to reduce the current to some limit (which I think is not much over 1 mA) AND then also displays what voltage it has had to reduce to, as well as displaying "<xxxx" in its display of the IR. With low resistances, the test voltage essentially falls to zero.

    Kind Regards, John
     
  12. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,177
    Thanks Received:
    157
    Location:
    Derry, Ireland
    Country:
    Ireland
    It measures the voltage drop to determine the impedance.
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,145
    Thanks Received:
    3,142
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    What? !!
     
  14. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,177
    Thanks Received:
    157
    Location:
    Derry, Ireland
    Country:
    Ireland
    That's what it does. It puts a load on the circuit and measures the voltage drop to calculate what the impedance is.
     
  15. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,567
    Thanks Received:
    2,550
    Location:
    Bedfordshire
    Country:
    United Kingdom
    That is one method that can be used to measure the impedance ( or resistance ) of an intentional circuit ( such as the end to end impedance of a ring final conductor ).

    It does not work well if at all for measuring the impedance of an unintentional circuit ( such as where current is flowing through damp insulation )
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,145
    Thanks Received:
    3,142
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    A load on what circuit? One only measures IR on a de-energised cable or circuit. The tester applies a voltage, but that only results in any current flowing if the insulation has a sub-infinite resistance and, even then, there is no 'load put on the circuit' by the tester.

    Also (the clue is in the 'R' of 'IR') what one measures is resistance, not impedance, since the measurement is undertaken using DC.
     
  17. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,177
    Thanks Received:
    157
    Location:
    Derry, Ireland
    Country:
    Ireland
    Sorry. I thought we were discussing loop testing for some reason. Didn't realise we were discussing insulation resistance testing.
     