Indeed - if you hunt out that old thread you'll see that we eventually did discover that at the time. However, IIRC, it was a slightly different type of question - in as much as my interest was in whether the 5% and 3% limits were percentages of the nominal or actual voltage. Even before we found the answer in the (then) BRB, it was pointed out that it would be unworkable for it to be anything other than U0, since whether or not one's VD was compliant could otherwise depend on when one measured the voltage.Right - very interesting. Do you remember when you were asking similar questions about determining volt drop and whether to use actual voltage or nominal voltage? I inadvertently found the answer in Appendix 12 BRB, now Appendix 4, 6.4 BGB., where it states that nominal voltage should be used.
As often seems to happen to me here, I am being accused of 'wanting' something ('wanting the regs to say something') when, in fact, I simply introduced a genuine question to which I did not know the answer. A couple of pages back, I wrote:Now you seem to be wanting the nominal voltage to alter so that it will be similar or equal to the actual voltage. If nominal voltage in tables is stated as 230V., and you seem not to think this applies universally, are you suggesting that the tables (and other values) are adjusted to take account of different nominal voltages on a daily or installation (or whatever) basis? How would you know if you had visited a premises on a particularly high or low voltage day?
I obviously do not want, and would not suggest, anything which resulted in figures, and hence potentially compliance/non-compliance, to vary from day to day, according to the prevailing supply voltage. That would obviously be crazy.There's also the question (to which I've never been sure of the answer) of whether the 'design current' of a circuit relates to what the current would be at nominal supply voltage, or whether it should take account of the maximum permitted supply voltage.
Quite!!It would be interesting to watch (from a bit of a distance) someone using an instrument which created a fault and actually measured the current flowing.Indeed so - I think/presume that they all do.It does it only by calculation.
There's a huge difference, and you are completely failing to see it.OK, I see your point, but I'm not sure that there is as much difference as you're suggesting ... ownership of handguns would not have to be illegal if everyone could be totally trusted not to do stupid things with them ('stupid things' including failure to take every reasonable step to prevent them getting into the 'wrong hands').
Fair enough; I take your point.There's a huge difference, and you are completely failing to see it.
I recently wrote:Right - very interesting.
Although there was a question sort-of implicit in that, I didn't actually ask it. If, with my installation's figures, you were completing an EIC, EICR or other form, would you record the PSC as what your meter said (685A) or, since you believe that all currents should be calculated using U0, would you manually calculate the figure using 230V and hence record 638.9A ?Note that 230/0.36=638.9 and that 246.8/0.36=685.6 ... so it appears the manual is telling the truth!
As a general concept, I agree totally with what you say, but I think that the sort of risk-benefit/need issues (for society as a whole) I mentioned do sometimes warrant consideration (in a rational and responsible way, not as a knee-jerk or in response to media pressures etc.), particularly when the 'need/benefit' (or even just 'desire') relates to a very small minority, yet the risk relates to the whole of society - something which is probably applicable in the case of hand gun ownership.A healthy society needs to be free from tabloid-induced knee-jerk legislation introduced in panic by stupid and ignorant legislators to destroy businesses, leisure pursuits and sporting activities because the people charged with implementing the existing, and perfectly adequate, legislation were grossly negligent.
You would record your meter reading - assuming its calibrated and you have used it for recording all the other test results. But for the example given it doesn't really matter does it?If, with my installation's figures, you were completing an EIC, EICR or other form, would you record the PSC as what your meter said (685A) or, since you believe that all currents should be calculated using U0, would you manually calculate the figure using 230V and hence record 638.9A ?
Kind Regards, John.
That's what I assumed.You would record your meter reading - assuming its calibrated and you have used it for recording all the other test results.
Obviously not - provided the PSC is less than 6,000A, the actual value is pretty irrelevant. If (way out of my zone of experience) the recorded meter reading were fractionally over 6,000A, the OPD rated at 6kA and the PSC calculated using 230V a little below 6,000A, then the difference clearly could matter.But for the example given it doesn't really matter does it?
So it's OK to oppress minorities, just because they are a minority?As a general concept, I agree totally with what you say, but I think that the sort of risk-benefit/need issues (for society as a whole) I mentioned do sometimes warrant consideration (in a rational and responsible way, not as a knee-jerk or in response to media pressures etc.), particularly when the 'need/benefit' (or even just 'desire') relates to a very small minority, yet the risk relates to the whole of society - something which is probably applicable in the case of hand gun ownership.
You seem determined to introduce daft "analogies".Given that you have introduced 'leisure pursuits and sporting activities', one might suggest that there are at least some parallels with fox hunting (a topic about which we can easily predict your views - with which I would agree). In that case, the feeling of a small minority that they have a need to be able to pursue such activities have (I would say correctly) been over-ridden by 'restrictive' legislation which is considered to be a benefit to society (in the widest sense) as a whole.
Quite.It's also hard to see how much further off-topic this can get.
I have always calculated PFC myself - not specifically for the reason you state (probably just a remnant from having meters which did not do it ).I recently wrote:Right - very interesting.Although there was a question sort-of implicit in that, I didn't actually ask it. If, with my installation's figures, you were completing an EIC, EICR or other form, would you record the PSC as what your meter said (685A) or, since you believe that all currents should be calculated using U0, would you manually calculate the figure using 230V and hence record 638.9ANote that 230/0.36=638.9 and that 246.8/0.36=685.6 ... so it appears the manual is telling the truth!
Fair enough - so, when you calculate it, do you use 230V for the calculation, and hence record a value for PFC or PSCC different from that displayed by your meter, or do you calculate on the basis of the voltage measured by the meter?I have always calculated PFC myself - not specifically for the reason you state (probably just a remnant from having meters which did not do it ).
For many calculations, and in the interests of consistency/practicality, I would agree. However, I don't believe that one should necessarily always use U0,'as a metter of principle', without any thought.I still maintain that using the same value of Uo for all calculations would seem logical.
Well, as I think you've pointed out yourself, it is an arbitrary (essentially 'political') number, used essentially for convenience. The fact that it is essentially 'meaningless' in engineering terms is illustrated by the fact that, in the UK, it changed from 240V to 230V without any change in supply voltages and, AFAIAA, no changes in any of the tabulated figures/limits etc. in documents like BS7671. The current drawn by, say, a particular shower did not suddenly change on the day that 'political' change occurred but, per your views, the design current of the circuit did change on that day. Whatever else that is, it's not engineeringOtherwise what is the purpose of a box on the EIC for nominal voltage. Also, if you disagree, then what IS nominal voltage other than a meaningless, useless number thought up for no reason?
I use 230 as that is what I think is meant by Uo/Ze (or Zs).Fair enough - so, when you calculate it, do you use 230V for the calculation, and hence record a value for PFC or PSCC different from that displayed by your meter, or do you calculate on the basis of the voltage measured by the meter?
I never have - that would mean a Ze of 0.03833ΩIf you use 230V for those calcs, and if you ever enounter very high PFCs (6kA or more), what would you do in the situation I recently mentioned
I would not - but that would be because the measurement is proving something amiss.... if your calculation using 230V was below 6kA, but the value displayed by the meter (calculated from actual voltage) was above 6kA, would you regard a 6kA OPD as being OK or not?
Perhaps not in a special installation where it would be necessary but in 'normal service' I think that is what we are told to do.For many calculations, and in the interests of consistency/practicality, I would agree. However, I don't believe that one should necessarily always use U0,'as a matter of principle', without any thought.I still maintain that using the same value of Uo for all calculations would seem logical.
Yes, but as there is only provision for the value to be recorded once.Well, as I think you've pointed out yourself, it is an arbitrary (essentially 'political') number, used essentially for convenience.Otherwise what is the purpose of a box on the EIC for nominal voltage. Also, if you disagree, then what IS nominal voltage other than a meaningless, useless number thought up for no reason?
The tables for maximum Zs, for example, were all adjusted by a factor of 23/24 so that the results are the same as before.The fact that it is essentially 'meaningless' in engineering terms is illustrated by the fact that, in the UK, it changed from 240V to 230V without any change in supply voltages and, AFAIAA, no changes in any of the tabulated figures/limits etc. in documents like BS7671.
No it didn't because, as I have previously said, it is not necessary to calculate for a shower circuit because the MIs state what CPD to use.The current drawn by, say, a particular shower did not suddenly change on the day that 'political' change occurred but, per your views, the design current of the circuit did change on that day.
True. It's not 'engineering' being told to use a particular CPD and CSA of cable (obviously allowing for the method of installation) but that's what we have to do.Whatever else that is, it's not engineering .