Is this birdsmouth type cut ok?

Discussion in 'Roofing and Guttering' started by Adviceseeker78, 23 Jun 2019.

  1. Adviceseeker78

    Adviceseeker78

    Joined:
    23 Jun 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    My builders seems to have done quite an irregular birdsmouth cut - is this acceptable for building regs?

    This is for a single storey extension with roof angle at 16 deg - wall to wall length is 3 metres so span is just over 3m.

    Thanks
     

    Attached Files:

  2. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    33,572
    Thanks Received:
    2,114
    Location:
    Staffordshire
    Country:
    United Kingdom
    No. That is terrible and amateurish. We try and limit the cut to 25% of rafter depth. You seem to only have 25% remaining.:eek:

    If there were joists sitting on that WP they would have rafter material protruding below the ceiling line. Horrendous. Sack the roofer and buy some new rafters.
     
  3. Adviceseeker78

    Adviceseeker78

    Joined:
    23 Jun 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    Arrgghhh. Thanks for posting. This is what another builder mate of mine said.

    The guy who did this is my main builder. Obvs very worried about the quality of the other work now.
     
  4. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    25,744
    Thanks Received:
    3,158
    Location:
    West Mids
    Country:
    United Kingdom
    You could add some ply gussets to reinforce the rafter.

    Nail plates may do the same thing, but you'd need the supplier or an engineer to confirm.
     
    • Like Like x 1
  5. Adviceseeker78

    Adviceseeker78

    Joined:
    23 Jun 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    I think the builder did it this way to get the angle for the roof tiles. Is there a building regs standard for this?
     
  6. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    25,744
    Thanks Received:
    3,158
    Location:
    West Mids
    Country:
    United Kingdom
    No. Building Regs are not standards.

    They're will be BS or EN standard, or the NHBC Standards may mention this or refer to the relevant BS/EN standard.

    Or you could get someone to calculate the loading and stress at the bearing and that will do.
     
    • Like Like x 1
  7. Adviceseeker78

    Adviceseeker78

    Joined:
    23 Jun 2019
    Messages:
    4
    Thanks Received:
    0
    Country:
    United Kingdom
    I’ve seen this image - maybe this is the plan to reinforce it this way? Would this work?
     

    Attached Files:

  8. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    25,744
    Thanks Received:
    3,158
    Location:
    West Mids
    Country:
    United Kingdom
    No. Google for plywood gusset and look at the images, and you'll need to cut two per rafter and scribe it around the wall plate to strengthen the rafter and also give it a better seat on the wall plate.
     
  9. noseall

    noseall

    Joined:
    2 Feb 2006
    Messages:
    33,572
    Thanks Received:
    2,114
    Location:
    Staffordshire
    Country:
    United Kingdom
    It begs the question: If they have allowed the rafter material (that which would be ordinarily removed on a regular BM) to protrude down into the room, why they never set the WP at that height, i.e. lower?
     
  10. Leofric

    Leofric

    Joined:
    9 Nov 2018
    Messages:
    907
    Thanks Received:
    71
    Country:
    United Kingdom
    Some say the birdsmouth cut out should be a maximum of 1/4 the depth of the rafter , others say 1/3. Too much has been cut out of your rafters and they need reinforcing as others say.
     
  11. Notch7

    Notch7

    Joined:
    15 Sep 2017
    Messages:
    9,583
    Thanks Received:
    842
    Location:
    Sussex
    Country:
    United Kingdom
    Prob because the wall went up, then the wall plate went on, then he scratched his head and wondered how to get to 16deg without any rework.
     
  12. Notch7

    Notch7

    Joined:
    15 Sep 2017
    Messages:
    9,583
    Thanks Received:
    842
    Location:
    Sussex
    Country:
    United Kingdom
    He could notch the joists too :ROFLMAO:
     
    • Thanks Thanks x 1
  13. catlad

    catlad

    Joined:
    29 Jul 2011
    Messages:
    3,408
    Thanks Received:
    450
    Location:
    Lancashire
    Country:
    United Kingdom
    That isn't worth pi$$ing around with, just start again.
    Preferably with another builder!
     