Is this cable suitable for connecting a 4kW double-oven to a 32A supply?

Discussion in 'Electrics UK' started by itm2, 22 Dec 2019.

  1. itm2

    itm2

    Joined:
    5 Apr 2011
    Messages:
    35
    Thanks Received:
    0
    Location:
    Surrey
    Country:
    United Kingdom
    I'm looking for electrical cable to connect a double oven to a 32A supply. The oven is rated at 4kW. Can anyone advise on whether this would be suitable? It's longer than I need, but the shortest that I could find in screwfix (which is my nearest outlet):

    https://www.screwfix.com/p/prysmian-6242y-twin-earth-cable-6mm-x-10m-grey/29733
    PRYSMIAN 6242Y TWIN & EARTH CABLE 6MM² X 10M GREY
    Brand Prysmian
    Cable Code 6242Y
    Cable End Type Bare
    Cable Length 10 m
    Cable Product Type Twin & Earth
    Cable Profile Flat
    Cable Voltage Rating 300/500 V
    CE Standard (Tested to EN...) BS 6004.
    Coil or Drum Coil
    Colour Grey
    Conductor Area 6 mm²
    External Diameter 13.1 mm
    Indoor/Outdoor Usage Indoor
    Manufacturer Guarantee 1 Year Guarantee
    Maximum Operating Temperature 70 °C
    Minimum Operating Temperature -15 °C
    Model No 20147221
    No. of Cable Cores 2-Core
    No. of Strands Per Core 7 Strands Per Core
    Pack Size 1
    Parent Colour Grey
    Pieces in Pack/Case 1
    Product Type PVC Flat Wiring Cable
    Sheath Colour Grey
    Supplier Manufacturer Helpline 08457 678 345
     
  2. Sponsored Links
  3. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,032
    Thanks Received:
    4,150
    Location:
    Retired to:
    Country:
    Portugal
  4. itm2

    itm2

    Joined:
    5 Apr 2011
    Messages:
    35
    Thanks Received:
    0
    Location:
    Surrey
    Country:
    United Kingdom
    Will a 2.5mm cable be adequate for a 4kW oven?
     
  5. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    6,972
    Thanks Received:
    531
    Location:
    London
    Country:
    United Kingdom
    Yes. 4kW is just over 20A, but not for long as ovens cycle on and off. 2.5mm cable is good for 27A.
     
  6. Ragnar_AT

    Ragnar_AT

    Joined:
    27 Apr 2018
    Messages:
    16
    Thanks Received:
    4
    Country:
    Austria
    I get 17.4A for 4 kW at 230 V. Did I miss anything?
     
  7. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,032
    Thanks Received:
    4,150
    Location:
    Retired to:
    Country:
    Portugal
    Sort of and not really.

    It will most likely be quoted at 240V.

    4kW @ 240V is in fact 16.7A which will be

    3.68kW @ 230V and 16A (which is probably not a coincidence)

    because the resistances of the oven are the constants - 14.4Ω, current and voltage are variables.
     
  8. Sponsored Links
  9. very_pointy_ears

    very_pointy_ears

    Joined:
    29 Mar 2005
    Messages:
    178
    Thanks Received:
    0
    Country:
    United Kingdom
    But if the OP is going to use 2.5mm T+E then they need to know to use a breaker rated at less than 32A
     
  10. OwainDIYer

    OwainDIYer

    Joined:
    5 May 2010
    Messages:
    4,545
    Thanks Received:
    695
    Location:
    Stirlingshire
    Country:
    United Kingdom
    Not necessarily. An oven is a fixed load which is unlikely to overload, and a 32A will probably still provide short-circuit protection. This must be proved by calculation.

    A larger cable would be prudent though, to allow for an appliance with a heavier loading in future.
     
    • Like Like x 2
  11. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,032
    Thanks Received:
    4,150
    Location:
    Retired to:
    Country:
    Portugal
    I expect he's done it by now.
     
  12. very_pointy_ears

    very_pointy_ears

    Joined:
    29 Mar 2005
    Messages:
    178
    Thanks Received:
    0
    Country:
    United Kingdom
    I'm not an electrician by trade but I would personally feel more comfortable using 6mm2 cable for this. Better to reasonably over-engineer than under-engineer in my (admittedly non-expert) view.
     
  13. very_pointy_ears

    very_pointy_ears

    Joined:
    29 Mar 2005
    Messages:
    178
    Thanks Received:
    0
    Country:
    United Kingdom
    Oh blimey I didn't notice that post was so old - it was showing at the top of the forum list so I assumed it was new ...
     
  14. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,032
    Thanks Received:
    4,150
    Location:
    Retired to:
    Country:
    Portugal

    There really is no need.

    1.5mm² is adequate for 16A.
     
  15. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page