just fitted TRV struggling to get rads on afterwards

Joined
17 Sep 2003
Messages
42
Reaction score
0
Country
United Kingdom
hi.

was very pleased to get a replacement rad fitted & TRV but now after bleeding all rads only the upstairs bedroom rads are on..bathroom is luck warm & no downstairs rads are on.../cant work it out,,,gut feeling is an air lock somewhere

any ideas

normal system with a tank..not combi

many thanks
 
Sponsored Links
hi....eurostar oil boiler..tank in air cupboard..grundfos pump

all rads are bled./.all rads have water in...how do i tell if the system is full>?

i found a bleed valve in airing cupboard....bled that...wonder if theres more somewhere..

when i turn heating on pump sound louder than normal...thanks for help
 
Sponsored Links
theres a big disc on the front of the pump (about 1 inch across) is that the bleed valve?
 
have a look at the FAQs at top of page, it will lead you.

there is a big silver slotted disc on the front of the pump.

turn off central heating, remove slotted disc, allow water to dribble from pump, also spin the shaft with a screwdriver, to check the pump rotates freely,replace slotted disc and turn on central heating
 
If it has a slot it's a screw - undo until water comes out.

See what speed it's set to . It can make matters better - or worse, to set higher.

Then close any rads which get warm. That'll force air into the other rads.
If any refuse, you have a sludge problem, like many many others.
 
cheers guys....all that bleeding & a nights sleep kicked the whole thing into life!
 