    A friend of mine has bought one of those kitchen mixers with a pull-out spray and has asked if I can install it. I took a cursory look at the instructions and have read the following.


    It could be a criminal offence to use this tap with water supplied by a Water Company. (The supply pipe is the one which brings the waters supply into your home and is directly connected to the public water main).


    This tap has an outlet on a flexible hose which, if left immersed in water could result in contaminated water being drawn back into the pipework if the supply pressure dropped. To prevent contamination of drinking water in the premises and in the water main, and to comply with the legal requirements of the UK plumbing regulations and byelaws (Water Regs 1999), both hot and cold water supplied to this tap must come from a storage cistern.


    Has anyone fitted this sort of item before and if so did both the hot and cold supplies really have their own storage cisterns? I cannot envisage having seen any sort of setup like that previously. Would appreciate any comments.
     
  2. Sponsored Links
  3. just pumps

    just pumps

    Joined:
    24 May 2016
    Messages:
    2,224
    Thanks Received:
    361
    Country:
    United Kingdom
    Thought they retracted when you stopped using them, have to admit I`ve never fitted one myself.
     
    • Thanks Thanks x 1
    • Like Like x 1
  4. jj4091

    jj4091

    Joined:
    1 Dec 2006
    Messages:
    4,949
    Thanks Received:
    451
    Location:
    Cumbria
    Country:
    United Kingdom
    • Thanks Thanks x 1
  5. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,173
    Thanks Received:
    1,410
    Location:
    North
    Country:
    United Kingdom
    It might just be bum covering, classing it as a higher risk fluid category, as they don’t where the tap is going to be installed, eg a butchers shop. I personally wouldn’t recommend it as you’re supposed to have access to potable (fit for human consumption) water available, and a tank fed would not meet this requirement.

    A worthy read?
    https://www.wras.co.uk/consumers/resources/glossary/type_auk3/
     
    Last edited: 29 Nov 2019
    • Thanks Thanks x 1
  6. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    7,558
    Thanks Received:
    2,100
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    Would need to check the regs again but I think dirty/soapy dish washer might be classed above CAT3 water therefore an air break would be needed for the cold water at least, if not the hot, if they are both mains fed.
    Strictly speaking running it from the mains wouldn't be allowed if it classed above CAT3 but a verifiable double check valve on mains fed, would certainly go some way .

    Usually these taps have a flexi pipe that has a weight attached to the pipe under the sink, that then pulls the tap head back into the tap when let go but I guess it could still sit in the dirty water and therefore a potential backflow contamination risk.
     
    • Thanks Thanks x 1
  7. Sponsored Links
  8. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,226
    Thanks Received:
    442
    Location:
    London
    Country:
    United Kingdom
    If you set the counterweight on the flexible hose so that the head on the end of the flexible hose is 20 mm above the spillover level of the sink you should be OK (AUK3 air gap). I'm fairly certain a double check valve is not considered a sufficient guard against contamination. A kitchen sink is likely to have fluid category 5 as they are often used for washing meat and poultry.

    As for using them with stored water, most houses in the UK wouldn't have sufficient head to allow many of these taps to work.
     
    • Thanks Thanks x 1
    • Like Like x 1
  9. chainsaw_masochist

    chainsaw_masochist

    Joined:
    6 Sep 2004
    Messages:
    965
    Thanks Received:
    22
    Country:
    United Kingdom
    Guys, just to convey my thanks for some very interesting comments. Suffice to say I persuaded matey to return the said mixer and obtain a straight forward, no messin' Franke job, sans extendable hose. I remain amazed that they can get away with selling this sort of thing.

    Thanks, again. :)
     
    • Thanks Thanks x 1
    • Like Like x 1
  10. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,786
    Thanks Received:
    3,084
    Location:
    Sussex
    Country:
    United Kingdom
    The water regs (vital for our health) are constantly being eroded by illegal imported fixtures/fittings.
    Take a look at Islamic douches, they used to be confined to Mosques but are now commonplace in homes....they are non compliant and there is no simple way to install them legally.
    Nothing is being done to prevent the sale or installation....:rolleyes:
     
    • Thanks Thanks x 1
    • Like Like x 1
  11. Chris_W

    Chris_W

    Joined:
    26 Sep 2019
    Messages:
    5,173
    Thanks Received:
    1,410
    Location:
    North
    Country:
    United Kingdom
    I am directly employed by LL and if I see one I always try to disconnect it telling them it’s an illegal installation, and if they don’t let me, then I would report them to my local water undertaker for them to deal with :whistle: also if it’s part of pipework I’m changing then I legally have to remove it, can’t reconnect it as I’m then in breach of regs. There’s too many people (including some colleagues) who don’t care about the water regs, I always tell them that the could be drinking foul waste, usually persuades them :LOL: we have some customers who “need” them as part of their religion, I have told managers not to ask me to install them unless they want the job spread out and costly :D

    We also have other trades undertaking plumbing bathroom suites and kitchens, all in Hep2o, not bothered about undue warming (hot pipe under cold), backflow prevention on shower heads etc :unsure:
     
    Last edited: 5 Dec 2019
    • Thanks Thanks x 1
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page