Yes you'd bond from towel rail to cast iron bath for instance.
How close does 'what' has the be from the appliance CPC - do you mean the point of bonding to the pipe/whatever?Rather than focus on where on the pipe the s. bond needs to be on the pipe, how close must it be to the appliance CPC ?
I stand corrected" 701.415.2 Supplementary protective equipotential bonding
Local supplementary protective equipotential bonding according to Regulation 415.2 shall be established connecting
together the terminals of the protective conductor of each circuit supplying Class I and Class II equipment to the
accessible extraneous-conductive-parts, within a room containing a bath or shower, including the following:"
That seems to be the implication of the regs.No not really , for parts that can be touched simultaneously, does the s.bond have to be made directly from the electrical item, say a class 1 light fitting or towel rail ?
That's true in bathrooms etc., but, for what it's worth, in a more general sense, the wording is slightly different..." 701.415.2 Supplementary protective equipotential bonding
415.2.1 Supplementary protective equipotential bonding shall include all simultaneously accessible exposed conductive-parts of fixed equipment and extraneous-conductive-parts including where practicable the main metallic reinforcement of constructional reinforced concrete. The equipotential bonding system shall be connected to the protective conductors of all equipment including those of socket-outlets.
I have subsequently clarified what I was intending to say - not that the point of bonding "did not matter" (which is what I erroneously wrote) but, rather, that what matters is the resistance (hence length of a given CSA) of the SB conductor - such that the lower that resistance (hence shorter the SB conductor) the better - and that means that the optimum point at which to bond the pipe (for lowest touch voltage until fault is cleared) is the point on pipe closest to the exposed-c-p being bonded, not the point closest to whatever is touchable (e.g. tap) on the end of the pipe.As for it not mattering where the SP conductor is connected to the pipe; ....
What you say is obviously true..... surely the farther it gets from the, for example, tap in a bathroom the less effective it must become until at the extreme it just becomes another CPC for the faulted appliance rather than an SB conductor for the tap.
As I've just written in response to EFLI, whilst that's certainly true, very much the same can be said of any supplementary bonding. Conductors do not 'know what they are' or 'why they are there', and the electrical effect of installing any SB will usually be to create an additional path in parallel with the circuit's CPC.That is what I was trying , clearly not that well, to express. Electrically no different to another cpc the further it gets away from the location ,
My take is that you make a judgement call.That seems to be the implication of the regs.
I'm not sure what people do if, say, there are multiple Class I items with exposed-c-ps on the same circuit. There will obviously be a CPC joining all their exposed-c-ps, but that would probably not satisfy the requirements for an SB bonding conductor - but I'm far from convinced that everyone would necessarily formally 'bond' all of the items (multiple Class I downlights on a low ceiling would be an example, if that ever happens)..
That is true. I would not regard it as a concept but the nearer to the MET the SB connection is, the less the conductor is an SB until it becomes only another CPC.However, given that the pipe itself is a conductor (and usually one with a much larger CSA than CPCs or SB conductor, you could say the same of any supplementary bonding - namely that the SB was merely providing "another CPC", since it provides an additional path from the exposed-c-p to MET in parallel with the circuit's CPC. I therefore don't think it is a very useful concept to invoke.-
Surely it must, or as above it is just another CPC (or unnecessary conductor).In any event, as I keep saying, I cannot agree that it is necessarily true that [paraphrasing you] "....as the point of bonding gets further from the tap, the effectiveness of the SB 'must become less' ".
I do not disagree but when moving farther away from the tap - or more importantly, nearer the MET, there must come a point when the conductor is no longer an effective SB.The "effectiveness of the SB" is at its greatest (i.e. lowest touch voltage) when the SB is the shortest possible (i.e. when bonding is to the point in the pipe closest to the exposed-c-p. If the point of bonding moves away from that point, in either direction (e.g. to get it 'closer to the tap'), such that the SB conductor becomes longer than 'the minimum possible', the 'effectiveness' of the SB will decrease (touch voltage will increase). Do you disagree with that?