Lifestyle LP241 replaced with Hive CH issue

OK managed to measure voltages (All AC voltages) this evening :)

HW + CW Both on (Boiler On). Orange = 240V, White = 240V, Grey = 0V

HW Only On. (Boiler On) Orange = 240V, White = 28V, Grey = 0V

CH Only On (Boiler off??). Orange = 0V, White = 240V, Grey = 15V
As said, CH only grey should be 230 volts, the valve
mid-position-valve.jpg
is an odd device, and it can result in some odd voltages. @stem has shown how it is wired, and the boiler is run direct from the tank thermostat when set to DHW or DHW plus CH, and the 230 volts at the orange is actually a back feed from the boiler.

So if SW2 is faulty, then you will not get CH on its own.
 
Yes I missed that point . I'll try an measure the HW off, HW on & CH on the terminals on the back of the Hive control unit. If they match those measured on the 3-valve, in particular grey HW off - then the Hive unit is suspect - I also verify this by refitting the LP241 and seeing if CH on works again as it used to.
 
I also realised there is a problem with the backplate, once the hub is removed to get access to the contacts, clearly you can't test if the unit is switching, lucky I have a wiring centre between the hubs, Thermostats_tonemapped.jpg allowing me to measure.

So assuming two channels, I would fit links 1771343030706.png if you then get CH you know the wiring to backplate is OK.
 