Err - we don't know what zone it's going to be in, so you can't say that for certain.Must be IPx4 and have no switch - you'll need a ceiling pull switch.
Only for any new concealed cables.Yeah, the RCD is mandatory now.
The advantage of (b) is that you could use an RCD spur which would mean your new concealed cable would comply with the regulations.If I had to go for option (b) I assume I would need a fused spur outside the zones?
Capping is for protection against plasterers' trowels only.I would be chasing the wall above the sink from ceiling down to fitting and running in the 1.5mm with at least capping over the cable.
You need to show them how you will comply with P1. It would be a good idea for you to first read Approved Document P for details of the path of least resistance, and the On-Site Guide and the Electrician's Guide To The Building Regulations.What do building control actually require from me before I proceed? Is it a statement of my intended work? sketches. Is there a simple guide for how you deal with this?
But if you are not creating a new circuit in the bathroom it doesn't have to comply with 701.411.3 - the regulations are not retroactive.30mA RCD protection is now required for ALL circuits in a bathroom, regardless of depth and/or bonding, see regulation 701.411.3.
The concealed cable will, which is why I said that making it a spur would be handy.So if you extend a circuit, the bit the you have added/modified will need a 30mA RCD.
Err - we don't know what zone it's going to be in, so you can't say that for certain.Must be IPx4 and have no switch - you'll need a ceiling pull switch.
Only for any new concealed cables.Yeah, the RCD is mandatory now.
Which bit?In the context, that's gratuitously pedantic.
But if you are not creating a new circuit in the bathroom it doesn't have to comply with 701.411.3 - the regulations are not retroactive.30mA RCD protection is now required for ALL circuits in a bathroom, regardless of depth and/or bonding, see regulation 701.411.3.
The concealed cable will, which is why I said that making it a spur would be handy.So if you extend a circuit, the bit the you have added/modified will need a 30mA RCD.
Err - we don't know what zone it's going to be in, so you can't say that for certain.Must be IPx4 and have no switch - you'll need a ceiling pull switch.
New concealed cables will need RCD protection because they are concealed, not because of the location.Agreed, regs are not retrospective, however the point I was making was that all circuits in a bathroom do require a 30mA RCD, which is why I went on to say the "bit the you have added/modified" will need a RCD. The depth and bonding issues still apply.
Sorry - it was the ceiling switch I was commenting on, not the IP rating....Even if it's located outside of Zones 1 or 2, accessories should still be fit for location. If there's even a remote chance the fitting would be splashed with water then its IP rating should be considered.
New concealed cables will need RCD protection because they are concealed, not because of the location.
The regulations are not retroactive.701.411.3.3 is un-ambiguous, 30mA RCD protection is required for circuits in a bathroom.
Even if the cable was on the surface and all bonding was in place you will still need a 30mA RCD for the modified part of the circuit in the special location of a bathroom!