Hi I am swapping my twin & e to 3 and e to get a neutral to the switches, so just checking do I just use the existing cable size or has anything changed and you all use a standard size now ?
Thanks
 
Sponsored Links
1mm will be fine on a modern installation with 6A or 10A mcb protecting the cabling. Don't forget that if you are running new cabling and it less than 50mm from finished surface and not in steel conduit the circuit will require rcd protection (it may already be protected but check before you start). Also remember safe zones
 
1mm will be fine on a modern installation with 6A or 10A mcb protecting the cabling. Don't forget that if you are running new cabling and it less than 50mm from finished surface and not in steel conduit the circuit will require rcd protection (it may already be protected but check before you start). Also remember safe zones
Thanks old wiring in ex council house around 25-30 years back but I got the cu renewed 10 years back and rcd/mcb protected
 