A small craft shop supplied from the owner's house via a 6 mm² SWA sub main. The sub main is supplied from a 16 amp MCB in the owner's house.
The 16 amp was chosen to limit the maximum load that the shop can take as well as protecting the SWA
The shop has a CU feeding two radials to sockets each with a 16 amp MCB and lighting from a 6 amp MCB.
Problem over the weekend. Staff in the shop have a 2 kW heater on radial and a 3 kW kettle on the other radial. This trips the 16 amp MCB in the house.
No power, till cannot be opened, card machine cannot be used.
No one at home so key holder for the house has to be called to open up and reset the MCB
Solution proposed.
Change MCB in house to 32 amp to protect SWA ( or 20 amp ) and fit a 16 amp MCB in the shop between SWA and the shop's consumer unit.
Question. How to fit the 16 amp MCB load limiter in the shop. There are 2 spare modules in the shop's CU but would it be acceptable to fit the MCB in there or would a separate housing be needed.
The 16 amp was chosen to limit the maximum load that the shop can take as well as protecting the SWA
The shop has a CU feeding two radials to sockets each with a 16 amp MCB and lighting from a 6 amp MCB.
Problem over the weekend. Staff in the shop have a 2 kW heater on radial and a 3 kW kettle on the other radial. This trips the 16 amp MCB in the house.
No power, till cannot be opened, card machine cannot be used.
No one at home so key holder for the house has to be called to open up and reset the MCB
Solution proposed.
Change MCB in house to 32 amp to protect SWA ( or 20 amp ) and fit a 16 amp MCB in the shop between SWA and the shop's consumer unit.
Question. How to fit the 16 amp MCB load limiter in the shop. There are 2 spare modules in the shop's CU but would it be acceptable to fit the MCB in there or would a separate housing be needed.