Had a call today, they could only get hot water with the heating switched on. When I got there it was working fine, but just before I left it started playing up.
With heating off, when you open hot water tap, boiler fires, then quickly goes off, then on and off etc and the water goes down the flow and not to the taps. When the tap is then closed, it continues to do this. Even when switching boiler off on the boiler power button it continues to do this!!
I even switched the spur off and on and with the tap off it started to do the exact same thing. The only way to get it to stop is by unplugging the motorised valve from the pcb and plugging it back in again.
In central heating mode the boiler is fine, but the problems start again once the tap is opened.
I took a reading across terminals m11.1 and m11.3 with a tap open and it was 0v, but with tap closed it was 230v.
Apparently the diverter valve (springs o-rings and other bits) was replaced a couple of weeks ago when the problem first occured
Is this pcb or motorised valve?
With heating off, when you open hot water tap, boiler fires, then quickly goes off, then on and off etc and the water goes down the flow and not to the taps. When the tap is then closed, it continues to do this. Even when switching boiler off on the boiler power button it continues to do this!!
I even switched the spur off and on and with the tap off it started to do the exact same thing. The only way to get it to stop is by unplugging the motorised valve from the pcb and plugging it back in again.
In central heating mode the boiler is fine, but the problems start again once the tap is opened.
I took a reading across terminals m11.1 and m11.3 with a tap open and it was 0v, but with tap closed it was 230v.
Apparently the diverter valve (springs o-rings and other bits) was replaced a couple of weeks ago when the problem first occured
Is this pcb or motorised valve?