I had main bonds out for Zs, and also I tested it with the soft facility, am i right in assuming a calculation of Zs is best for the reading to be recorded on EIC ? or is there other precautions i shld take into acount before accepting the result?
You have to be very careful!
r1 and r2 mean something different to R1 and R2!
r1 is the end to end resistance of the phase conductor
r2 is the end to end resistance of the CPC
(r1+r2)/4 = R1+R2 if all sockets are on the ring. Spurs will be slightly higher.