Mains water stop cock affects pressure on combi boiler

Discussion in 'Plumbing and Central Heating' started by Jupiter01, 15 May 2020.

  1. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,990
    Thanks Received:
    41
    Country:
    United Kingdom
    Hi All,

    I was helping may parents by replacing a basin tap. I shut off the mains water tap inside the house to carry out the work. I then turned the water back on.

    I then noticed that the water pressure on the combi boiler was almost down to zero. Is this expected? I thought the combi boiler had its own closed circuit of pipes and am unclear on how this could be affected by the mains water.

    I'd appreciate your insight on this. Thanks
     
  2. Sponsored Links
  3. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,438
    Thanks Received:
    1,102
    Country:
    United Kingdom
    Do you mean the pressure gauge on the boiler?
     
    • Like Like x 1
  4. Jupiter01

    Jupiter01

    Joined:
    30 Mar 2015
    Messages:
    2,990
    Thanks Received:
    41
    Country:
    United Kingdom
    Yes, pressure gauge on the boiler. Since topping it up again, the pressure has been fine for a couple of weeks now.
     
  5. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,438
    Thanks Received:
    1,102
    Country:
    United Kingdom
    Just coincidence, nothing to do with the basin tap.
     
    • Like Like x 1
  6. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,585
    Thanks Received:
    2,551
    Location:
    Bedfordshire
    Country:
    United Kingdom
    If the filling loop is still connected then maybe in the absence of mains pressure at the closed filling loop valves these valves are letting by from pressurised boiler system to zero pressure mains.
     
    • Like Like x 1
  7. Sponsored Links
  8. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,438
    Thanks Received:
    1,102
    Country:
    United Kingdom
    Then they would surely let by the other way when the mains is back on and over pressurise the heating system.
     
    • Like Like x 1
  9. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,585
    Thanks Received:
    2,551
    Location:
    Bedfordshire
    Country:
    United Kingdom
    It seems that when the valve is shut the ball is pressed against the seal by mains pressure. When boiler pressure exceeds mains pressure the ball is pressed away from the seal. Hence the arrow indication on the valve indicating which way the valve should be fitted
     
    • Like Like x 1
  10. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,438
    Thanks Received:
    1,102
    Country:
    United Kingdom
    I have never had an instance of turning the mains off and finding that the heating system pressure has dropped to zero because both filling loop valves are passing. Have you?
     
    • Like Like x 1
  11. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,585
    Thanks Received:
    2,551
    Location:
    Bedfordshire
    Country:
    United Kingdom
    I have seen where putting pressure on a ball type valve in the wrong flow direction can result in the valve "weeping".

    Vaguely recall this weeping was ( is ) one of the reason why the filling loop should be removed when not re-pressuring the system
     
    • Like Like x 1
  12. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page