    Dismiss Notice
MCB FAULTY? Help!
Discussion in 'Electrics UK' started by JayDiy, 29 May 2018.
  1. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    Fantastic, I’ll check this on Saturday and let you know how I get on, cheers
  2. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    Right guys I have finally got to the bottom of this, there are no loose connections anywhere, so I opened up the cooker connector box and behind it I could see that the wire seemed to be coming through the plaster horizontally and going toward the adjacent unit where I have another microwave/2nd oven, so I removed this appliance and to my surprise I found a fused spur switch with 13amp fusewhich had blown, which now explains why the 40amp mcb didn’t trip, I am very annoyed that the electricians would do such a thing. So anyway it’s now sorted. Thanks guys for all your help. Cheers!
    • Like Like x 2
  3. JohnW2
    JohnW2
    28 Jan 2011
    40,789
    Thanks Received:
    2,526
    Buckinghamshire
    Country:
    I'm glad that you found the FCU and have, at least temporarily, solved your problem!
    However, do you know why the fuse blew. There's usually a reason, which means that (since you presumably have done nothing to remove any reason) there is a good chance that the new fuse may also blow in due course.
    Kind Regards, John
  4. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    The reason it blew is because it shouldn’t be connected to a 13 amp fused spur, the cooker is rated at 40 amps so I have now replaced it with a proper cooker switch as it’s protected by the mcb.
  5. EFLImpudence
    EFLImpudence
    7 Jul 2010
    28,048
    Thanks Received:
    3,018
    Retired to:
    Country:
    Portugal
    Was that the first time you had ever used the cooker?
    Are you sure the cooker supply is actually routed throught the 13A fuse?
  6. JohnW2
    JohnW2
    28 Jan 2011
    40,789
    Thanks Received:
    2,526
    Buckinghamshire
    Country:
    As EFLI has implied, if a load which drew 40A was connected via a 13A fuse, it would never have worked (fuse would have blown first time it was switched on) - was that the case?
    The instructions for the cooker may say (almost certainly unnecessarily) that it should be connected to a "40 A supply", but it is very unlikely that it would actually require a supply anything like that large.
    Do I take it that the 'cooker' really is a 'full cooker' (i.e. an oven plus hob)? Ovens alone are often designed to run of a 13A supply (e.g. through a plug/socket) and, even those which need a bit more than that probably don't usually draw enough current to blow a 13A fuse.
    Kind Regards, John
  7. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    No, I’ve been using cooker for a few months now without any problems, and yes was actually routed through the 13amp fused socket because I tested it and also confirmed it was the fatter cooker cable coming into it. I’m ****ed off with those electricians who did this in first place.
  8. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
  9. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    Yes it’s a 5kw oven and the secondary unit is a oven/microwave, both connected to this supply, looking back when the fuse blew I did have both ovens operating at same time, maybe this caused some overload. All good now.
  10. JohnW2
    JohnW2
    28 Jan 2011
    40,789
    Thanks Received:
    2,526
    Buckinghamshire
    Country:
    Fair enough. By application of the accepted principle of diversity, A 5kW oven, in itself, would be deemed to take ('an average of') about 13.5A, which would never blow a 13A fuse. However, if this was perhaps the first/only time you had also run the two appliances simultaneously (through the same 13A fuse) that might well be the reason why the fuse blew on this occasion.
    It takes something like 22A to blow a 13A fuse in an FCU (which means that a sustained 5kW load {which an oven would never actually present} would quite probably not blow it), and that corresponds (with application of 'diversity') to a peak (i.e. the total stated 'ratings' of the appliances) total load of around 11.5 kW
    Kind Regards, John
  11. ban-all-sheds
    ban-all-sheds
    27 Aug 2003
    69,787
    Thanks Received:
    2,857
    London
    Country:
    Are you sure it wasn't a kitchen fitter?
  12. securespark
    securespark
    11 Jan 2004
    32,750
    Thanks Received:
    953
    Country:
    What is the maximum load of the oven?
  13. JohnW2
    JohnW2
    28 Jan 2011
    40,789
    Thanks Received:
    2,526
    Buckinghamshire
    Country:
    Is that not what the "5kW" the OP told us will be?
    If so, as I said, that corresponds to around 13.5A after diversity (a bit less if, as is likely, the "5kW" relates to 240V). Even without diversity, it would be a fraction under 22A, so a 13A BS1362 would be unlikley to blow even if it were drawing 5kW continuously (which obviously wouldn't happen). However, with a microwave load on top of that, it might well blow the fuse.
    Kind Regards, John
  14. JayDiy
    JayDiy
    11 Aug 2017
    26
    Thanks Received:
    Country:
    You may be right they were general builders doing everything under supervision of the contractor.
  15. Taylortwocities
    Taylortwocities
    28 Jul 2006
    18,324
    Thanks Received:
    1,813
    Oxfordshire
    Country:
    LMFAO
    :LOL::LOL::LOL::LOL::LOL: