Is there a guide as to when to use different types (B, C, D ) of MCB's please.
crafty1289 said:where the Zs are stupidly low
securespark said:crafty1289 said:where the Zs are stupidly low
I'd say a low Zs was sensible, not stupid!!
Adam_151 said:securespark said:crafty1289 said:where the Zs are stupidly low
It depends how low, I think that anything too far smaller than 0.08 at the board might start to make our undersized CPCs fail the adiabatic on an MCB protected circuit, especially if you want to try and make 2.5/1 comply...
Hmm. I suppose if the EFLI is very low, the psc would be sky-high, exceeding the 6K breaking capacity
securespark said:This is something I've never fully understood. How can a circuit with a mega -low Zs (and consequently sky-high psc) be protected by breakers with a lower breaking capacity?
plugwash said:did this recognised company give a cert? and if so can you scan and post it so we can look it over.
D10s seems seriously over the top for lighting and C32s seems like a poor choice for rings (though both could be acceptable if Zs figures are low enough). It seems almost like they just threw in whatever they could find.
you also wan't to find out what that cable they used for the emergency lights was. Is there a BS number printed on it?