MCB?

Surprisingly a 10KA breaker is only has a servicable rating of 7.5KA, it can interrupt a 10KA but might not survive to break another day :D .
 
Spark123 said:
Surprisingly a 10KA breaker is only has a servicable rating of 7.5KA, it can interrupt a 10KA but might not survive to break another day :D .

LOL! Or as in this case, "make"!

What is the likely surviveable current for a 6kA MCB?

Cheers,

Howard
 
A 6KA breaker should be able to withstand the full 6KA, according to GN3 that is.
 