Hello All,
Out of curiosity, lets say you are running a twin and earth cable from the CU in conduit (up 2m into a ceiling), clipping it to a joist in an insulated loft, then inside capping down to a 'point', which method would you consider it ?

Thanks for any advice.
 
Sponsored Links
If it were running in contact with insulation for more than 500mm, then Method 4.

If not in contact with insulation, Method 3.

If embedded direct into plaster or masonry, Method 1.
 
Thanks secure,

I suppose what I meant to say is do you put all the methods used in the circuits 'wiring' (in that tiny space on test forms :LOL: ) ??

Thanks for your time.
 
Sponsored Links
No, just the most severe, I expect, because when you design a circuit, you use the most severe method in the calculation.
 