mira combiforce 415 exposed PROBLEM PLEASE HELP

Joined
8 Mar 2010
Messages
2
Reaction score
0
Location
Bristol
Country
United Kingdom
hiya
ive had this shower for around a year now was going fine until the other day, when turned on its nice and hot for only around 10 seconds then goes luke warm ive tried all the taps in the house and they work fine nice and hot any suggestions ????
would be gratefull
 
It may be that the pressure on the hot water diapragm in the boiler is not enough to turn on the burner. you may need to replace the diaphragm. The warm water you get at first is a heat plug from inside the boiler when the heating has been on, but then the burner has not lit and all you get is cold water.

:(
 
hi rite when the hot water taps are on the burner fires up as it should and when the shower is turned on
the hot pipe is just exposed so i can just touch it gets hot for a few seconds then just stays luke warm like the shower so dosent seem like its getting hot traveling up the pipe
the heating works fine nice and hot its just the shower???
 
then its not a shower issue if the hot pipe is only luke warm.
as already said check the boiler with the shower runing its probably cutting out.
 