you can use a combined Feed and Expansion pipe now (formerly you had to use two pipes).
Not so hasty, this is an old boiler and is unlikely to have an additional overheat thermostat. Some manufacturers allowed combined F&E but not all especially older models.
Remember in a fault condition the boiler will be boiling the water and will have trouble replenishing it with steam going up the feed pipe.