• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

NEFF Built in Double (Under) Oven & Electric Hob

Joined
1 Jan 2007
Messages
3
Reaction score
0
Country
United Kingdom
I have purchased a Neff Built in (Under) Double oven and Neff Electric Hob - is it possible to wire these appliances to the same 30A supply?
 
Hi MK,
Can you tell us the ratings ( amps or watts ) of the hob and oven ?
Thanks.
 
Oven: Neff U1722
Hob: Neff T1213

I know that the Main Oven on the Neff has a total load of 4Kw as the for the Hob:

Front left rating (kW) 1.2
Back left rating (kW) 2.2
Front right rating (kW) 2
Back right rating (kW) 1.2
 
10.6k's.

46.09A.

Some say install a circuit for each because for times like Xmas, you need full load.

Others say you can use diversity thus:

First 10A of load + 30% of remainder + 5A if cooker switch has adjacent socket outlet.

Therefore your 10.6kW load, with diversity applied, can be run from a 30A circuit.

What cable is the 30A circuit wired in? And how long is it? (The cable.... :roll: )
 
Many thanks for the prompt reply!
i'm not sure on the thickness of the cable without taking a look, I presume the standard thickness....... as for the length of the cable its about 9 / 10 metres.
 