Discussion in 'Plumbing and Central Heating' started by DIYer007, 21 Jan 2017.

  1. DIYer007

    DIYer007

    Joined:
    21 Jan 2017
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi - I have just bought a NEST 3rd gen system and I am trying to work out the wiring diagram for which wire goes where, I would be very grateful for any advice. I have attached the photo of my Potterton EP3002 program wiring harness.
     
  2. Echo the husky

    Echo the husky

    Joined:
    25 Mar 2011
    Messages:
    2,476
    Thanks Received:
    326
    Location:
    Devon
    Country:
    United Kingdom
    You appear to have a standard Y Plan system, so you need to check that diagram in the manual. You will need to put the 2 wires that are in terminal D in a separate connector block, they will not connect to the nest. As you have so many earth wires they too will need to go in another separate connector block. Your existing terminals are:
    N - neutral
    L - permanent live
    1 - hot water off
    3 - hot water on
    4 - Heating on
    5 - common for heating

    Look through the manual at the y plan wiring diagram and with the information above you should be able to work out what goes where, I'm not doing everything! Post back here to confirm or if you are stuck.

    There is not much room in the Nest receivers I would probably fit all the wires in a box and then run a single cable to the Nest. Or install a back box in the wall to contain everything. There must be none of the coloured wires showing outside of the nest enclosure. If it starts looking like the wiring on this page, you are doing it wrong!
     
    • Thanks Thanks x 1
  3. Sponsored Links
  4. DIYer007

    DIYer007

    Joined:
    21 Jan 2017
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you so much for this advice - i am going to have a go this afternoon. I will update you to let you know how successful i am.
    Again, many thanks you are a star!
     
  5. oilhead

    oilhead

    Joined:
    29 Nov 2009
    Messages:
    1,873
    Thanks Received:
    426
    Location:
    Shropshire
    Country:
    United Kingdom
    The base plate of the EP3002 is also the junction box or wiring centre. Ideally you need to transfer this to a 10 way junction box, and introduce the Nest wiring into this.
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page