    Hi, I'm having a new boiler installed in a new location the other side of the house. The current setup is an old convential boiler with pump/diverter valves etc.

    The current circuit is a 6a MCB feeding the boiler / burglar alarm. Coming from the consumer unit is 2x 1.5mm cables on that MCB feeding a fused connection for the alarm and the other cable wired straight to the boiler wiring with no FCU that I can see at all which isnt good. At this point the wiring goes off to thermostats and pumps and will be a big task to identify so the plan is to get rid of the lot at the consumer unit.

    I have an easy route to the new boiler location (under the floor) and a roll of 2.5mm T+E, would there be any issue terminating this to the 6a MCB other than being uncommon? I would also replace the wiring to the FCU for the alarm with 2.5.

    Thanks
     
  2. Iggifer

    Iggifer

    Joined:
    8 Sep 2011
    Messages:
    4,637
    Thanks Received:
    587
    Location:
    Warwickshire
    Country:
    United Kingdom
    Irrespective of any other issues, there is absolutely no point using 2.5mm.

    1mm would be fine. 1.5mm would be more than enough, 2.5 is ridiculous.

    Why not just add a spur either above the CU or where the existing boiler is and then just run the new cable from there?
     
    • Thanks Thanks x 1
  3. Sponsored Links
  4. deadshort

    deadshort

    Joined:
    20 Sep 2014
    Messages:
    2,086
    Thanks Received:
    211
    Location:
    uk
    Country:
    United Kingdom
    Hi, yes 2.5mm would be fine and as you already have some even better ! It would be an issue if you wanted to use a lower gauge cable on a larger breaker! 2.5mm will handle 27a

    so, no problem with 6a !


    Kind regards,


    ds
     
    • Thanks Thanks x 1
  5. LiGhTfasT

    LiGhTfasT

    Joined:
    27 Mar 2013
    Messages:
    29
    Thanks Received:
    0
    Location:
    Lancashire
    Country:
    United Kingdom
    I already have a good 20m of 2.5 on a roll in the garage so will cost me nothing and will have no other use for it. I didnt want to put it on a spur off the kitchen ring since it already has its own circuit. Thought it may also come in handy one day if needed with a bigger MCB.

    Thanks for the replies :D
     
  6. Sponsored Links
  7. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    47,639
    Thanks Received:
    3,100
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    ...except that 2.5mm² is what the OP has!
    Unnecessarily large, sure - but as deadshort has said, not 'ridiculous', particularly if that's what one has! You're right that 1.5mm² would be more than adequate. So, electrically speaking, would be 1mm² - but, unless you could successfully argue that a boiler counts as 'lighting', it would probably not be compliant with regs!

    Kind Regards, John
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page