At random selected a boil, it was a logic, but that does not matter the manual says:-
What you are looking at is the "Part Load" what can it throttle down to.
Boilers running at low output are more efficient to one running at full output, but if the boiler has to cycle on/off/on/off to keep the output low enough then the efficiency falls.
In other words too big is just as bad as too small.
All the people who quoted should have done whole house heat loss calculations and sized boiler on results.
Why? That's only half a job, much more important is how the home is used.
So if one leaves the house at 7 am and you do not return until 6 pm, it is recovery time which is important, but retired and in the home 24/7 then losses more important. Add to that is all rooms are used for whole of 24 hours, like with an old peoples home, then the requirements are well over what is needed when 90% of the time only 2 rooms are used at any one time.
So I want living room warm, plus the toilet, and to a lesser extent the kitchen, those radiators are unlikely to be fully turned on, so if the 4 radiators (assuming 2 in living room) add up to 4.5 kW then the 12 kW boiler could modulate to 3.9 kW so that would seem logical but the 15 kW only modulates to 4.9 kW so it would end out using a mark/space ratio turning on/off rather than modulating down.
Some makes of boiler can modulate better than others, so you may find one make which can range from 3.5 to 20 kW so you have best of both, but if the total radiator size is not big enough to use all that energy, then rather pointless.
So my house, 14 heated areas, and 15 radiators, in the main I will only want to heat half of the heated areas, so the radiator size needs to be at least double the size of the boiler. With my life style likely four times the size would be better.
So we look as a scenario, arriving home at 6 pm, to a house maintained at 17°C and want it to heat up to 21°C by 6 pm, lucky TRV heads like the Wiser can calculate when to turn on to achieve that, but if it will take an hour, then need to start reheating at 5 pm, but if it takes 2 hours, the 4 pm, and the larger the radiator in the room to be used first the faster the reheat time, and there is no need to reheat all rooms to 21°C by 6 pm only the first room to be used, so you can set second room to be at temp by 6:30 pm and third room by 7:00 pm so only heating one room at a time.
But as you can see, more down to life style to what the home loses.