New Boiler: Getting contradictory advice about size

The problem now is that the fitter who is doing this is nervous that there might not be sufficient gas pressure to drive an 18kW and wants to stick with what is there now (12).
He should be able to calculate pressure drop at the increased gas flow. Also he could measure the pressure at the boiler with the current one at maximum output, to give an idea of any likely problem.
 
The mistake I made here is when I said that my current 12kW can heat the house on the coldest of days.. Thats true.. But it takes time and thats with 30% of the radiators off... I have nothing to compare it too and don't know whats possible.. But for me, it doesn't feel like there is enough 'umph', in the current system. It gets there for sure, over time.. But I believe its struggles in extreme cases.
You keep asking/saying the same thing.

The fiter can do a heat loss calculation to determine just what size you need. Or fit the Vokera Pinnacle 20s which which modulate low enough for whatever is needed.
The problem now is that the fitter who is doing this is nervous that there might not be sufficient gas pressure to drive an 18kW and wants to stick with what is there now (12)
The fitter should be able to check that very easily.
 
You keep asking/saying the same thing.
I am not asking anything. I was just looking to close this discussion with a final update incase it helped anyone in the future.. But people still keep telling me I am wrong..
 
A heat loss calculation / estimate of some sort should really be the start of any boiler selection process.
 
Or fit the Vokera Pinnacle 20s which which modulate low enough for whatever is needed.
That's a system boiler, current one is heat-only, so installation likely to be more complicated. And there's a lot to be said for heat-only, where the parts of the system are separate and accessible.
 
I am not asking anything. I was just looking to close this discussion with a final update in case it helped anyone in the future.. But people still keep telling me I am wrong..
But you raised the additional point about the nervous fitter!
 
But you raised the additional point about the nervous fitter!
It was just an additional comment.. Sorry that mentioning another point caused offence.. I think we need to wrap this one up... We arn't getting anywhere.. Everyones points are taken on board.. However, sometimes its not as easy as implied, when you live in a rural area and the selection of fitters is small and they want to make a selection based on previous experience... I have very limited options and all of done work on the exact same houses before and have a pre-determined idea of what size is needed...
 
Add up the outputs of all the radiators, that could be found online easily enough. Would give you an indication of the boiler size requirements.
 
At random selected a boil, it was a logic, but that does not matter the manual says:-
1793809696608.png

What you are looking at is the "Part Load" what can it throttle down to.
1793809811489.png

Boilers running at low output are more efficient to one running at full output, but if the boiler has to cycle on/off/on/off to keep the output low enough then the efficiency falls.

In other words too big is just as bad as too small.
All the people who quoted should have done whole house heat loss calculations and sized boiler on results.
Why? That's only half a job, much more important is how the home is used.

So if one leaves the house at 7 am and you do not return until 6 pm, it is recovery time which is important, but retired and in the home 24/7 then losses more important. Add to that is all rooms are used for whole of 24 hours, like with an old peoples home, then the requirements are well over what is needed when 90% of the time only 2 rooms are used at any one time.

So I want living room warm, plus the toilet, and to a lesser extent the kitchen, those radiators are unlikely to be fully turned on, so if the 4 radiators (assuming 2 in living room) add up to 4.5 kW then the 12 kW boiler could modulate to 3.9 kW so that would seem logical but the 15 kW only modulates to 4.9 kW so it would end out using a mark/space ratio turning on/off rather than modulating down.

Some makes of boiler can modulate better than others, so you may find one make which can range from 3.5 to 20 kW so you have best of both, but if the total radiator size is not big enough to use all that energy, then rather pointless.

So my house, 14 heated areas, and 15 radiators, in the main I will only want to heat half of the heated areas, so the radiator size needs to be at least double the size of the boiler. With my life style likely four times the size would be better.

So we look as a scenario, arriving home at 6 pm, to a house maintained at 17°C and want it to heat up to 21°C by 6 pm, lucky TRV heads like the Wiser can calculate when to turn on to achieve that, but if it will take an hour, then need to start reheating at 5 pm, but if it takes 2 hours, the 4 pm, and the larger the radiator in the room to be used first the faster the reheat time, and there is no need to reheat all rooms to 21°C by 6 pm only the first room to be used, so you can set second room to be at temp by 6:30 pm and third room by 7:00 pm so only heating one room at a time.

But as you can see, more down to life style to what the home loses.
 