I need some advice ..I need to install new wiring in the attic / loft I found a cable that used to supply power to the immersion water heater tank located in the upstairs bathroom I was wondering if I could use this cable and create a new radial line for the attic's ligthing and power sockets The idea is to fix a 30 amp junction box in this cable and once the ligths and sockets are installed returning the cable to the original junction box therefore creating a new radial circuit .
 
Sponsored Links
That would not be good practice, because you'd lose lighting when the circuit is tripped by, for example, a faulty appliance.

For the lighting circuit you'd be better off extending the upstairs lighting circuit into the attic.
 
Yes, you have the right idea.
Dont mess with your existing lighting.
Your old immersion should be fed by a 16amp breaker from c.unit, take the cable from this in immersion cupboard and put it onto a garage type c.unit, not expensive, then run your power sockets from the 16amp and take your lighting from the 6amp. You will probably get a unit with the rcd as well so happy days..
 