Need some advice.
Had the CU upgraded to 17th edition as part of loft conversion, all been signed off and BC cert has arrived.
Have a question on power sockets, the sockets are all under 32A MCB'S, i just noticed it now, is this ok? I though its normally 16A/20A MCB'S?
Perfectly fine if they are ring circuits, which is most likely, but I can't tell from here.
Not fine if they are radial circuits, which is less likely, but again, I can't tell from here.
So, the work was notified and certified?
Therefore you have a copy of the installation certificate?
This will tell you if the circuit has been configured as a ring.
It might be.
Or it might not be.
True. But as a blanket statement like that, it's incorrect.
For the benefit of the OP, if they are radials wired in >4mm² cable, they're fine on a 32A OPD. If the cable is <4mm², and it's a radial on a 32A MCB, that is indeed, not fine.
It might be.
Or it might not be.
Seeing as we're splitting hairs....
Not fine, in that it might need some consideration as to whether the cable size is adequate for the OPCD.
What considerations would make a 2.5mm² cable adequate for a socket radial on a 32A device?
The OP would need to consider whether the cable size as installed is less than 4mm or is at least 4mm.
The OP might also like to consider whether the circuit is a ring or a radial.
"Consider - look attentively at"