Hi, this involves a new oven and hob supply in a kitchen. I'm aware of Part P and notification. Is the following acceptable please?
Am I correct in thinking T&E burried direct in plaster in a concrete wall has the same CCC as "clipped direct" = 47A for 6mm T&E?
If so, is it acceptable to feed 6mm T&E from a 45A RCBO in the CU to a 45A cooker switch (with drop to outlet for a 7.8kw hob) AND then continue from the first switch to another 45A cooker switch which has a drop to outlet for an oven rated at 3kw please?
The 45A RCBO should protect the installation and although the total load could be ~47A, diversity would mean that would be unlikey to happen and 47A would take a very long time to trip a 45A RCBO - is that correct please?
Am I correct in thinking T&E burried direct in plaster in a concrete wall has the same CCC as "clipped direct" = 47A for 6mm T&E?
If so, is it acceptable to feed 6mm T&E from a 45A RCBO in the CU to a 45A cooker switch (with drop to outlet for a 7.8kw hob) AND then continue from the first switch to another 45A cooker switch which has a drop to outlet for an oven rated at 3kw please?
The 45A RCBO should protect the installation and although the total load could be ~47A, diversity would mean that would be unlikey to happen and 47A would take a very long time to trip a 45A RCBO - is that correct please?