    Hi I need to add a new socket in my kitchen can I run a cable from an existing socket going down and then accross to the left?
     
  2. jonbey

    jonbey

    Joined:
    17 May 2012
    Messages:
    4,221
    Thanks Received:
    239
    Country:
    United Kingdom
    I think the official answer is, get an electrician to do kitchen electrical work.

    But if DIY, then you can probably do that - does the new socket need to be far from the existing? If not, you could just put it right next to it?
     
  3. Kevin hayes

    Kevin hayes

    Joined:
    30 Jan 2020
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    It's not far approx 1.5m to the left it's to house a built in microwave
     
  4. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    2,566
    Thanks Received:
    480
    Location:
    Durham
    Country:
    United Kingdom
    DIY wiring in kitchens (in England anyway- Wales is different) is not notifiable but has to be done properly.
    First thing- is the existing socket on a radial circuit (20A fuse/breaker at the consumer unit) or a ring final circuit (32A fuse/breaker at the CU)- either type could have 2 x 2.5mm or larger T & E cables coming into it. Or is it a spur from an RFC? You need to find out- if it is a spur then you cannot spur from it UNLESS the entire spur is powered via an FCU.
    Second, is the new cable to be chased in or surface mounted? If chased in then the circuit must be protected by an RCD at the consumer unit (an RCD socket is not acceptable since that would not protect the buried cable)
    Third, buried wiring straight across from the existing socket to the new socket is fine, straight up or down from existing to new is fine, across then down is not acceptable. If the wire is on the surface then that's fine. The common way round this in a kitchen is to chase drop the wire straight down to below worktop level, run it on the surface below the worktop then chase up to the new socket (or not even chase if it is hidden by a built-in appliance). Because 1 part of the new wire would be buried you would still require RCD protection at the CU.
     
  5. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    5,492
    Thanks Received:
    399
    Location:
    London
    Country:
    United Kingdom
    Why not? The existing socket gives a safe zone for the across bit and the new socket gives a safe zone for the down bit.

    What you cannot do is go diagonally.
     
  6. oldbutnotdead

    oldbutnotdead

    Joined:
    11 Jan 2013
    Messages:
    2,566
    Thanks Received:
    480
    Location:
    Durham
    Country:
    United Kingdom
    Oh yeah, course it does :) . Prefer not to do it but tis compliant...
     