there is nothing I can think of that can create a system pressure imbalance that can create a 2 port valve, that doesn't have any issues, to clunk
Me too, unless there's a serious feck up in the piping!

there is nothing I can think of that can create a system pressure imbalance that can create a 2 port valve, that doesn't have any issues, to clunk
Probably allready suggested but maybe run with the 2 port actuator removed and the valve left manually opened for a few days.Perhaps it is?
Can only assume that's where it's been teed in... As it should be.
Probably allready suggested but maybe run with the 2 port actuator removed and the valve left manually opened for a few days.
Yes, that’s the cream one to assist the Megaflo. The original on the heating side was red (which makes sense) got replaced with the gray one (less so).Is the above EV in addition to the Megaflo air bubble?? so has nothing to do with a (red) EV installed if a heat only boiler.
It is, as per IMG_1488, there’s big 22mm t-off from the cold feed to the Megaflo after the pressure control unit. Glad that aligns with expectations.Looks like it, so should have been installed downstream of the expansion valve on the cold feed to the Megaflo.
I don’t think that has been, but makes sense & we’ll test for a while. My expectation is that with the NC valve held open we won’t have the issue.Probably allready suggested but maybe run with the 2 port actuator removed and the valve left manually opened for a few days.
I don’t think there’s enough space above the flow pipe from the boiler to do that. It’s too close to the ceiling.Also, the Spirovent is installed between the pump discharge and the MPV, maybe better to have it installed before the pump inlet.
Couple/three other things which we’ve considered:
* Is there an Integrated Flow Check valve in the Wilo Pico pump that might allow a pressure difference
- No evidence the PICO pump has such a device; plus hard to see how it would have this effect
* Might the pump benefit from a run of the de-aerator function?
- Pressed the button & waited 10 mins while it ran, will advise IDC
* Could the old Califei(?) air-vent at the top right of IMG_1490 be holding some air?
- We were told to keep the black plastic bleed screw locked down to avoid air being sucked into the system
PS: And thanks for the continued input. Very much appreciated by both of of us.