The SUPPLY NEUTRAL must go into the N terminal at the top of the RCD, NOT into the Neutral bar. The way it is currently wired, the neutral current is bypassing the RCD, which will trip as it only has current on the live side.
Wired correctly, the current through both live and neutral conductors from the supply goes through the RCD which thus sees the same current in both directions and does not trip.
There is far too much copper on show there.