No DHW demand signal

Joined
2 Jul 2014
Messages
6
Reaction score
2
Country
United Kingdom
Hello and thanks for any help.

I have a Navien system boiler configured as S Plan.

Everything has been working fine for 2 years until the other day when the boiler no longer fires for DHW only.

CH works fine and the valve on the DHW circuit also operates correctly. I am still able to get hot water by ensuring CH and DHW are set to the same firing schedule.

But if the schedule is DHW only, the valve operates but the boiler does not fire.

Some other information:

Boiler controller always says the DHW demand is off, no matter what.

Connected to an unvented cylinder with a codice dual high limit cutoff thermostat. Thermostat clicks correctly and I have tried pushing the reset button.

On the Navien control centre the thermostat is connected to the "cyl" terminals

My assumption is that somehow the DHW demand signal is no longer triggering (or at least not making it to the boiler). Is there a simple way to test this?

Also, I know I am not qualified to work on an unvented cylinder I am just trying to figure out where the problem lies, if it's the cylinder / thermostat I'll get a plumber in, but if it's something else / simple, maybe I can fix it myself.

Thanks for any advice.
 
Thanks. I did wonder about that.

So the valve has 5 wires, live, neutral, earth, grey and orange. Live neutral and earth are all connected to the relevant connectors but but orange and grey are cut and disconnected. This is by design, the original installer has tapped over the ends of these so I know they have not become disconnected accidentally. I think this might be because the Navien wiring centre connects to the boiler wirelessly? So the switched live from the valve it not needed?

The only connections to the valve are as shown here.
 

Attachments

  • PXL_20250209_113811130~2.jpg
    PXL_20250209_113811130~2.jpg
    144.3 KB · Views: 118
Well, it took all day but I figured it out. Don't know how it happened, but the demand control on the boiler was set to thermostat - which I assumed was correct, but it actually needed to be set to"wiring centre". I don't understand how the wiring centre option works, but everything working as expected now. Just heated a tank of water and it switched off at the right temperature.

Maybe this thread is useful to someone else in the future. Thanks for the reply.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top