Worcester boiler 24 CDI, boiler does not fire when there is demand for DHW otherwise it fires up

Discussion in 'Plumbing and Central Heating' started by Zehroni, 15 Feb 2021.

  1. Zehroni

    Zehroni

    Joined:
    25 Nov 2005
    Messages:
    394
    Thanks Received:
    1
    Country:
    United Kingdom
    This boiler dose not fire up when there is a demand for DHW, but the it fires up when there is a demand for CH. The diverter valve works ok its head extends when there is a demand for DHW and engages with the microswitch on top of it. Also the pump is working but the boiler does not fire. I also tried to the run CH and open the hot tap and as soon as I do that the boiler stop firing. Any idea please
     
  2. Sponsored Links
  3. Zehroni

    Zehroni

    Joined:
    25 Nov 2005
    Messages:
    394
    Thanks Received:
    1
    Country:
    United Kingdom
    I did more test on the boiler today and found out that both the fan and the pump work for a short time then they stop when there is a demand for DHW. this gave me the indication that the microswitch is working and does its job by passing the order to the PCB to fire the boiler However, when they stop, I could hear clicking noise inside the boiler as it wants to fire but it could not. this led to to think of the DHW sensor and as soon as I replaced it with one I took off Hallstead boiler, it started working as it should. happy days
     
  4. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,927
    Thanks Received:
    3,143
    Location:
    Sussex
    Country:
    United Kingdom
    You do realise that thermistor temperature/resistance profiles can vary considerably and you may have compromised the safety.
     
    • Thanks Thanks x 1
  5. Zehroni

    Zehroni

    Joined:
    25 Nov 2005
    Messages:
    394
    Thanks Received:
    1
    Country:
    United Kingdom
    good point, however, I believe most combi boilers work on the same principle when it comes the DHW output. also it is sensor responsibility to to shut the boiler down when the temperature accedes the limit. furthermore, both sensors looks exactly the same , identical
     
  6. Sponsored Links
  7. Gasguru

    Gasguru

    Joined:
    9 Sep 2005
    Messages:
    11,927
    Thanks Received:
    3,143
    Location:
    Sussex
    Country:
    United Kingdom
    You believe wrong...there can be a vast difference in thermistor profiles...at 20 degrees some might be only 10s of ohms others 100,000s of ohms.
    Fit the correct part.
     
    • Thanks Thanks x 1
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    20,628
    Thanks Received:
    8,023
    Location:
    Lanarkshire
    Country:
    United Kingdom
    New PCB time
     
    • Thanks Thanks x 2
    • Like Like x 1
  9. Zehroni

    Zehroni

    Joined:
    25 Nov 2005
    Messages:
    394
    Thanks Received:
    1
    Country:
    United Kingdom
    Many thanks for the advice, worcester bosch genuine part has been fitted
     
    • Like Like x 1
  10. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    20,628
    Thanks Received:
    8,023
    Location:
    Lanarkshire
    Country:
    United Kingdom
    And the part was ?
     