Also a 3A BS 1362 fuse would provide absolutely no protection to the device. It is for protection of the cable. If internal fusing was required, it certainly wouldn't be a BS 1362 fuse!
So fitting one was only about complying with manufacturers' instructions - it was never, and could never, have been about providing protection for the current using equipment!
So fitting one was only about complying with manufacturers' instructions - it was never, and could never, have been about providing protection for the current using equipment!