    Hi,

    We had our approximately 7 year old logic combi 30 boiler moved earlier this week. It was only along the wall about 6 foot so no major pipe changes and this was done by a registered gas safe engineer.

    The following night we tried to turn our central heating on. The first two in the chain got semi warm but stayed mostly cold at the bottom and the return pipes remained cold. No other radiators heated up at all. We bled the radiators, this did nothing. We tried balancing them. Nothing.

    The engineer came back and suggested its a blockage as the boiler fires up for about 50 seconds then powers off. After a few minutes it fires up again then this repeats itself. He said to empty the radiators, run the system through using the filling loop then refill. This did nothing.

    We have tried closing the valves to each radiator. This does nothing.

    Today we put some sludge removal in the system. This also did nothing except make the boiler make some horrible gurgling noises. We bled the radiators (not that much air came out at all) and tried again. Again, it still keeps just firing up for 50 seconds or so then resetting.

    We think it's unlikely that it's a blockage because although the boiler itself is around 7 years old, the radiators and 90% of the pipework are only 2 years old. We haven't had them on since March (ish) but they worked perfectly then.

    The pressure is absolutely fine and doesn't budge. The pump sounds like its working and is hot when the CH is being called for.

    Interestingly, whenever we've drained the system down relatively close to trying them, the return pipe feels warm. This suggests there's no blockage right?

    No error codes come up on the boiler either.

    Absolutely no idea what to try next - is it a new boiler job?

    Sorry for the long post but its been a very cold, frustrating few days!
    Thanks in advance.
     
    Last edited: 10 Oct 2020
  2. Sponsored Links
  3. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,166
    Thanks Received:
    1,278
    Country:
    United Kingdom
    Sounds like a lack of circulation. Check the circulator .
     
  4. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,521
    Thanks Received:
    9,719
    Location:
    Lanarkshire
    Country:
    United Kingdom
    get the installer that moved the boiler back
     
  5. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    We did - he's the one who said it's a blockage. We messaged him today and he said to try the sludge remover and if that fails then it's most likely a boiler issue. To be fair, we did only put the sludge remover in an hour ago so maybe I'm just being impatient. Stupid question but can we actually hold him liable to this? He left a certificate saying it was all visually fine but doesn't seem keen on coming and fixing it.
     
  6. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    How would we go about checking it? It sounds like it's working but I guess it could just not be running properly.
     
  7. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Also the engineer felt it when he came the other day and said 'it feels like it's working' whatever that means.
     
  8. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,627
    Thanks Received:
    1,118
    Country:
    United Kingdom
    You can't tell by simply feeling it. I'd be getting the fitter back to carry out some basic checks, first one being the pump.
     
  9. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,521
    Thanks Received:
    9,719
    Location:
    Lanarkshire
    Country:
    United Kingdom
    sludge remover as you call it will not clear a blockage, all chemical cleansers need circulation to work
     
    • Like Like x 1
  10. Sponsored Links
  11. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    That's what the engineer called it we emptied the system, put the cleaner in then topped it up again, will this not have circulated it enough?
     
  12. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,166
    Thanks Received:
    1,278
    Country:
    United Kingdom
    If there is no circulation ,the chemical will do nowt.
     
    • Like Like x 2
    • Thanks Thanks x 1
  13. Alec_t

    Alec_t

    Joined:
    18 Mar 2017
    Messages:
    758
    Thanks Received:
    132
    Location:
    Wales
    Country:
    United Kingdom
    Perhaps the pump impeller has seized, even if the pump sounds as though it's working. Have you tried running the pump at its maximum speed?
     
    • Like Like x 1
  14. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,436
    Thanks Received:
    535
    Location:
    London
    Country:
    United Kingdom
    1. It certainly sounds like a circulation issue. The boiler fires, heats the water, tries to send it round the circuit. It doesn't lose enough temperature (because it isn't going anywhere), the boiler detects there is too big a difference between flow and return temperatures, so shuts down. Water cools, differential falls within limits, boiler fires and off it all goes again.
    2. Because its a combi, all the usual suspects (pump, zone valves) are within the boiler. So it must be one of two things:
    2a. A genuine blockage within the heating circuit.
    2b. A problem within the boiler.
    3. Things to check on the heating circuit:
    3a. That the flow and return valves, under the boiler, are both fully open.
    3b. That any magnetic filter, usually on the return to the boiler, has both its valves open.
    3c. Beyond that you'd be looking for a pipework blockage. You could:
    3ci. Try flushing through as your plumber suggested. The filling loop is most likely attached to the return pipe, so you will be flushing in the reverse direction to normal flow. Ideally you would disconnect the flow pipe from the boiler and direct it to a drain, to avoid flushing through the boiler. However, not necessarily a DIY activity, so you would need to drain through a radiator drain point.
    3cii. While flushing, do the whole system, then shut down all but one radiator, flush that one on its own, then move on to the next in turn. If doing that close both valves on each radiator but the one you are doing, making a note of the number of 1/8ths of a turn required to close the lock shield valve. When finished make sure you open all the lock shields to their original settings.
    4. Things to check on the boiler (by a gas safe engineer only).
    4a. That the diverter valve is working properly.
    4b. That the pump is working.
     
    • Thanks Thanks x 2
    • Like Like x 2
  15. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Not sure how to do this but after running the CH for an hour or so the pump is too hot to much, I assume this is a cause for concern and it could be/is overheating? Thanks
     
  16. DavidR52

    DavidR52

    Joined:
    10 Oct 2020
    Messages:
    7
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for such an in depth reply. All valves are open. We've tried draining each radiator individually as suggested and that didn't work. The pump is too hot to touch after running for an hour or so, so an uneducated guess would be that the pump (or something in it) is overheating. Whether as a result of a faulty pump or a block in the boiler system I'm not sure. I've put forward to the engineer that it could either be the diverter or the pump - hopefully he comes back but he seems more unwilling to come and fix it each time I message him.
     
  17. terryplumb

    terryplumb

    Joined:
    8 May 2017
    Messages:
    6,166
    Thanks Received:
    1,278
    Country:
    United Kingdom
    Is the pump a grunfoss ? Show us a pic .
     