How long is the new horizontal pipe run ?
Is there any other horizontal run's ?
Is there any other horizontal run's ?
When you backfill you need to keep an eye on the F&E tank. The over flow pipe might not accommodate all the water flow rate that you are adding.
You say there is no slope on the horizontal pipe.
Part of the operation of a gravity system requires a small slope so that air is naturally expelled.
The "head" on a gravity system is very small, perhaps just 100 mm if you are lucky and that's why it needs large bore piping.
Perhaps Sajeel can explain why you put PTFE tape on the compression nut threads?
Tony