No power to boiler?

Sponsored Links
Sponsored Links
That is where you should be looking, your boiler takes its power supply direct from the boilermate 2000 terminal 5 is neutral 6 is live and 7 is switched live, see if you have power at these terminals
I do find your advice bizarre.You think giving gas testing advice to ameteurs is a no no but you are quite happy giving electrical testing advice to complete novices who obviously have not a clue.Bizarre and dangerous.
 
I do find your advice bizarre.You think giving gas testing advice to ameteurs is a no no but you are quite happy giving electrical testing advice to complete novices who obviously have not a clue.Bizarre and dangerous.
What is dangerous about re setting a breaker ?
 
I removed the 5 amp fuse from the Boilermate 2000 it had blown. Replaced today and the boiler in the garage is back on and working. Thank you.

Thank you for your contributions especially icnmcd & dilalio. Thank you both for your time and interest I really appreciate it.
 
That is where you should be looking, your boiler takes its power supply direct from the boilermate 2000 terminal 5 is neutral 6 is live and 7 is switched live, see if you have power at these terminals
Are you on drugs?....The above is not resetting an MCB!
 