Noise in radiators and pipes - thermostatic valves

Joined
27 Feb 2004
Messages
5
Reaction score
0
Country
United Kingdom
I have recently moved into a 1930s house with (what I was told) a one pipe central heating sytstem and a combi boiler. The thermostat was in the living room very near a radiator. The living room was nice and hot but upstairs remained fairly cold. I had the thermostat removed and thermostatic radiator valves fitted (Mistral which I have never heard of).

Now I have tapping and wooshing noises in some radiators (which is annoying in the bedroom since it sounds like a dripping tap) and knocking in a pipe which can go on for hours at a time. These noises, apart from very brief knocking in the pipe when the heating was turned on, were not there before the TRVs were fitted. The plumber says noises are normal in any system but I did not have any in my old house with a 30 year old central heating system.

Help
 
Sponsored Links
Sounds like your TRV's are 'chattering'.
This is normally because they have been fitted on the return pipe instead of the flow pipe.
You need to change the valves around or buy dual flow which can be fitted to either side
 
Thanks, I spoke to the plumber last night and he said the TVRs could be fitted either end of the radiator. The installation guidance for the TVRs said they are bi-directional and can be fitted either vertically or horizontally in the flow or return . For best performance it is recommended that the head is fitted horizontally, which I have never seen and they haven't been fitted that way but with the head upright. I'll have to check with the plumber again but he doesn't seem keen on coming back to sort it out.
 
Sponsored Links
If you have read on the manufacturers instructions that they are indeed dual flow then the problem lies elsewhere!
However if they are a cheap make (I always fit Honeywell) they could still be the source of the noise.
I would be inclined to ask your plumber to revisit as the noise is clearly unacceptable given the fact that prior to fitting you did not have a problem
 
Thanks Bahco, I'll try and get him to come round again, although he is not keen. Have you ever heard of Mistral TVRs, made by Yorkshire Fittings? In my previous house I had Drayton, which were fine.
 
do you mean these?
mistral_trv_t.jpg


the "blurb" says

Thermostatic radiator valve
- Designed for 2 pipe systems
- Comes with 15mm olive and 8mm and 10mm reducing kits
- Reversible flow
- Decorating cap included
 
Yes Breezer, that's the one. So its sounds like its no good for a one pipe system. Where can I get the blurb from?
 
:oops: sorry they have run out of blurb, you have had all that was available, but it came from here
 
Have you tried turning down the other side radiator valve down to see if it make any difference.
 
Thanks for the tips, I'll try turning downthe other side of the radiator (the lockshield valve?)
 