Non-bidirectional RCD/RCBO feeding sockets, should they get a code C2 with EICR?

That's a new one on me. Where did it come from, since I can't find it in any version of BS7671?

No matter what you (or 'we') may 'hope', and as I've said, it it is surely the case that there are countless millions of RCDs (presumably 'unidirectional') out there in service (including well over a dozen in my house) which do NOT bear any such marking, isn't it?

For that reason, I find it hard to understand how any 'regulations' about plug-in inverters could possibly address this issue - if many/most people don't know (and probably can't ascertain) whether their RCDs are unidirectional or bidirectional, they can hardly be expected to comply with regulations that would require that knowledge ?! ;)
Spot on, I can't see how it can safely work. And it does not matter what amendment 3 says, manufacturers are not going to recall products to add to them the load etc.

As to "Line" is that a miss print? see page 9 it does it seem to require RCD/RCBOs to be labelled, but as far as plug in solar goes, that label must be readable without opening the CU, which with most it is not.
 
Spot on, I can't see how it can safely work. And it does not matter what amendment 3 says, manufacturers are not going to recall products to add to them the load etc.
As I said, I can't see how it can/could 'work' at all, 'safely' or otherwise - at least for a very long time, since there are so many unlabelled RCDs in service out there!
As to "Line" is that a miss print? see page 9 it does it seem to require RCD/RCBOs to be labelled, but as far as plug in solar goes, that label must be readable without opening the CU, which with most it is not.
Ah - your quote came from Amd 3 - I can't have looked at that :-) What you say is correct. However, nearly all people buying 'plug-in solar' kit will probably know even less about BS7671 (or Amd 3 thereof) than they do about the unidirectional/bidirectional issue in general - so, again, if the kit is going to be sold directly to members of the general public, it doesn't look as if any of this 'regulation' will achieve anything!
 
As I said, I can't see how it can/could 'work' at all, 'safely' or otherwise - at least for a very long time, since there are so many unlabelled RCDs in service out there!
Yes, we could require electricians doing an EICR to label either sockets or CU as OK or not OK for solar, but that would take 5 years to get all rental properties marked up.
 
Yes, we could require electricians doing an EICR to label either sockets or CU as OK or not OK for solar, but that would take 5 years to get all rental properties marked up.
True, for rental properties there could be a requirement for sockets to be labelled as you suggest, if the existing legislation were modified accordingly. However, I'm not sure that would achieve much if tenants could go out and buy plug-in solar systems, since there would be no workable way of forcing them to take any notice of the labels.

... and, of course, it's almost inevitable that some owner-occupiers would also buy such kit - and I don't think that (even if it would achieve something -see above) it would be remotely thinkable to create new legislation that forced all dwellings to have 'labelled sockets' !!
 
and, of course, it's almost inevitable that some owner-occupiers would also buy such kit
The rental sector leaves the occupant with no control as to if RCDs are fitted, or RCBOs are fitted, he has to live with what the landlord has provided. He can't add sockets or FCU, or install anything.

As a result we need rules and regulations to make the occupant safe. As his only other option is to move house to one which has the safety features fitted.

The owner-occupier however can simply call an electrician to fit a suitable inlet for his solar, he could also DIY if he wishes, there is nothing to stop him, or someone he asks for help from, removing the CU cover and seeing what is fitted. In fact likely does not need to even do that, he will have the installation certificate which lists type.

I did look for what is what and AI came up with:- 1780052825350.png which seems to list the part numbers of RCBOs which are bidirectional, so if this is included with the installation instructions, then the user can check his unit is safe to use.
 
The rental sector leaves the occupant with no control as to if RCDs are fitted, or RCBOs are fitted, he has to live with what the landlord has provided. He can't add sockets or FCU, or install anything. ... As a result we need rules and regulations to make the occupant safe.
OK, but a requirement (per your suggestion) to 'label' sockets would surely not be enough to achieve that - the only guaranteed way 'to make tenants safe' (at least, 'as safe as possible') would surely be to introduce legislation that required all sockets in rental properties to be protected by bidirectional RCDs, wouldn't it?
 
OK, but a requirement (per your suggestion) to 'label' sockets would surely not be enough to achieve that - the only guaranteed way 'to make tenants safe' (at least, 'as safe as possible') would surely be to introduce legislation that required all sockets in rental properties to be protected by bidirectional RCDs, wouldn't it?
Exactly, which is why I started the thread. Google fusebox rcbo rtamb, and we see this 1780055103491.pngwhich is bidirectional where this 1780055202620.pngone is unidirectional easy to identify as the test button swaps from top to bottom. But as I looked at other makes, even the data sheet does not say which they are, only the picture tells one, with "out" written against the terminals. Which needs the CU cover removing to read it.

As to even if all MCBs are bidirectional I don't know? Seem to remember something about the arc chamber, and it's needing to be before the trip coil? 1780056608523.png We see this typical diagram of a MCB and the terminals are labelled output. I think it is unlikely to cause a problem working the wrong way around, but we simply don't know.
 
I've been trying to avoid much discussion about 'details' (particularly about 'what is theoretically possible'), since I think that detracts from my main point - which is that, particularly when 'major decisions' are to be made (like 'to ban' something - or, at the other extreme, to 'require/demand'something), those decisions should be based on information/data/evidence about what is actually seen to happen, in practice, in the real world - rather than considerations of 'what is theoretically possible'.
Ah, the "wait till there's actual evidence of harm before acting" approach.
Yeah, I think this bridge will be safe, I've never had one of my designs collapse before. Sure, don't worry about this DIY reactor in the back garden, I've never had one of mine go wrong before. Don't worry, I've never had a submarine collapse before.. OK, some sarcastic hyperbole there, but you get the drift ?

• It's hard to argue that shoving something with wrong size pins into a socket risks damaging the socket in various ways - whether that's damaging the contacts such that a fire is more likely in the future, or damaging the shutter and defeating a safety feature.
• It's hard to argue that having something which easily deforms such that it's "earth" pin can be used to open the shutters without blocking access to the L&N contacts doesn't defeat a safety feature.
• It's hard to argue that having a device which opens the shutters and has holes which give ready access to the L&N contacts doesn't defeat a safety feature.
• It's slightly harder to argue that having these covers will instil a false sense of safety because many people will not recognise the extra risks they create over and above any risks already present. But my opinion is that it's a valid argument to say that people are likely to be less cautious about child safety with these things fitted even though there are demonstrated risks not present with an uncovered socket.
• It's more of a stretch to argue that using these covers changes attitudes to "uncovered" sockets, possibly in a bad way.

So there we have a number of clearly demonstrable risks, even if there's little or no evidence of those risks realising into events, which are totally avoidable. Against that are some rather tenuous claims that some of these devices might make an already "reasonably" safe socket safer.
Both of us are familiar with the principle of ALARP, and I could not argue that adding avoidable risks is in any way ALARP.
BS1363 dates from when I think we had more respect for BSI and the standards setting process, and I would credit them with having considered the options and come up with something that was deemed ALARP, if you consider the RP part to include "and won't just annoy users into bypassing a feature" like some safety functions can end up as.
Having said that, to briefly remind you of something I've written in the past as regards 'inserting plugs upside down', what BS1363-2 requires (of sockets, include those in 'extension leads) seems (at least to me!) to be rather (very!) odd ...

The only requirement regarding placement (relative to 'edge' of the plate/whatever) of the 'apertures' to receive plug pins appears to relate to the L& N pins, but not the earth one .....

View attachment 415404

... as I've said before, unless I'm missing something (like a corresponding requirement relating to the earth pin receptacle), that appears to mean that it would be perfectly possible to have a compliant socket (with earth pin 'receptacle' fairly close to edge) into which the earth pin of a compliant plug could be inserted with the plug 'upside down' if the socket were attached to a surface pattress box or was one of the outlets of an 'extension lead', hence allowing something like this (as mentioned by you) that I once illustrated...

View attachment 415405
Going from memory, I was sure there was something about the size of sockets to prevent upside-down insertion of the earth pin. I don't have time to dig out the BS and look. Separately, there are rules around the size of plugs and sockets to make it hard to touch the L&N pins while it is partially inserted (along with the revised version which requires partially insulated pins.)

No matter what you (or 'we') may 'hope', and as I've said, it it is surely the case that there are countless millions of RCDs (presumably 'unidirectional') out there in service (including well over a dozen in my house) which do NOT bear any such marking, isn't it?

For that reason, I find it hard to understand how any 'regulations' about plug-in inverters could possibly address this issue - if many/most people don't know (and probably can't ascertain) whether their RCDs are unidirectional or bidirectional, they can hardly be expected to comply with regulations that would require that knowledge ?! ;)
I think we all agree that no regulations will help because users will ignore them. Even banning the sale wouldn't help given the ease of buying direct via various online sites that appear to not care about product safety laws and the lilke.
OK, but a requirement (per your suggestion) to 'label' sockets would surely not be enough to achieve that - the only guaranteed way 'to make tenants safe' (at least, 'as safe as possible') would surely be to introduce legislation that required all sockets in rental properties to be protected by bidirectional RCDs, wouldn't it?
Please don't give them ideas for any more regulations :eek:


As to even if all MCBs are bidirectional I don't know? Seem to remember something about the arc chamber, and it's needing to be before the trip coil?
I can't see there being any problem with the typical design of MCBs in CUs. It doesn't really matter which way round the trip and contact are - the contact is still breaking the current, and the system needs to break a fault of any polarity, and quench any ensuing arc. Unlike the RCDs, there's typically no electronics to get damanged.
 
Exactly, which is why I started the thread.
Indeed - but what you have highlighted is almost an 'impossible' situation ....

IF one believes that plug-in inverters cannot be used safely if plugged into circuits protected by unidirectional RCDs then, given the countless millions (probably 'hundreds of millions') of in-service sockets protected by such RCDs, the only really 'rational' approach would be to 'ban' such inverters - and, as Simon has said, even that would be far from foolproof.
 